A 2-ton air conditioner typically requires a 20-amp breaker. This ensures the electrical circuit can handle the load while providing the necessary power for the unit to function properly. It's important to consult with a qualified electrician to determine the appropriate size breaker for your specific AC unit.
You will need to use #8 wire.
For a 50 amp breaker to an AC unit, you would typically use 6-gauge wire. It is important to consult local electrical codes and the manufacturer's specifications for the AC unit to ensure the correct wire size is used for safety and proper operation.
No, it is not recommended to replace a 35 amp breaker with a 40 amp breaker for an AC unit. Breakers are designed to protect the circuit and the equipment, so using a higher rated breaker can lead to overheating and potential damage. It is best to use the correct amperage rated breaker for the equipment.
Yes, it is recommended to keep both the AC breaker and furnace breaker on, especially during the respective seasons when they are in use. This ensures that the units are powered and can function properly when needed.
The sizing of a breaker is dependant upon the size of the wire it protects. The size of the wire is dependant upon what the load current in amps is. Without the amperage and wattage and the voltage of the appliances an answer can not be given. W = A x V, Amps = Watts/ Volts.
You will need to use #8 wire.
For a 50 amp breaker to an AC unit, you would typically use 6-gauge wire. It is important to consult local electrical codes and the manufacturer's specifications for the AC unit to ensure the correct wire size is used for safety and proper operation.
Your ac contractor or engineer will determine the correct size.
Read the literature for the ac condensing unit, or the tag on the outside of the unit. Minimum circuit ampacity= minimum breaker, wire and fuse size. Maximum circuit ampacity= the maximum size. Your circuit breaker, wire size and disconnect fuses should all be at or between those 2 numbers.
2.5 ton
the answer is 1.11 ton
The size of room is enough wich is suitable for capacity of 1.5 Ton A/C The size of room is enough wich is suitable for capacity of 1.5 Ton A/C
P=VI here P=8000 Watts v=220 V I=8000/220 = 37 A so you should use 37A Breaker
45
A circuit breaker is easier to design for ac than dc because alternating current (ac) naturally goes to zero 100 or 120 times per second and this helps to extinguish any arc. Therefore an ac circuit breaker would not be suitable for dc assuming the same voltage and current ratings.
No, it is not recommended to replace a 35 amp breaker with a 40 amp breaker for an AC unit. Breakers are designed to protect the circuit and the equipment, so using a higher rated breaker can lead to overheating and potential damage. It is best to use the correct amperage rated breaker for the equipment.
Yes, it is recommended to keep both the AC breaker and furnace breaker on, especially during the respective seasons when they are in use. This ensures that the units are powered and can function properly when needed.