answersLogoWhite

0


Want this question answered?

Be notified when an answer is posted

Add your answer:

Earn +20 pts
Q: What is the current per phase on a 415v 2.2kw three phase motor connected in star?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

Can a single phase motor be wired to a three phase soft start?

No, a single phase motor cannot be directly connected to a three phase soft start. A single phase motor requires a single phase power supply, while a three phase soft start is designed for three phase motors. Using the correct soft start for the motor type is essential for proper operation and protection of the equipment.


How do you use a one phase motor in place of a three phase motor?

To use a single-phase motor in place of a three-phase motor, you would typically need a phase converter to convert the single-phase power supply into three-phase power. Alternatively, you can replace the entire motor with a single-phase motor that has similar specifications as the three-phase motor. It's important to consult with an electrician or engineer to ensure compatibility and safety.


Can 3phase source supplies single phase load?

Yes, a 3-phase source can supply a single-phase load. In this scenario, only one phase and the neutral conductor would be used to power the single-phase load. The other two phases would not be connected.


Why neutral cross section is half the phase in three phase cable while it has to carry current of summation of all phase..?

In a three-phase system, the neutral conductor only carries the unbalanced current resulting from the imbalances between the three phases. Since the sum of the three phase currents is zero in a balanced system, the neutral conductor's current will be half the current in each phase conductor when there is full load. This is due to the cancellation of currents in a balanced system.


Why the neutral cable takes high current than the phase lines in three phase installation?

In a balanced three-phase system, the current in the neutral wire should ideally be minimal as the three phase conductors carry equal and opposite currents that cancel out in the neutral wire. However, if the loads are unbalanced, the neutral wire may have higher current due to the uneven distribution of power among the phases. This can happen when loads on each phase are different or when single-phase loads are connected between a phase and neutral, leading to increased neutral current.

Related questions

What is the phase current of a three phase 2.2kw 415v motor connected in star?

The line current would be the same if the motor were connected in delta. The current can be based on the rule of thumb which says 7 amps must be allowed for a 1-HP single-phase motor on 240 v. A 2.2 kW motor is three times as powerful, and on a three-phase supply of the same voltage (240/415) it would draw 7 amps.


What is the current in star connection?

If a motor is connected in star, the current in the motor winding will be equivalent to the line current. If the motor is connected in delta, the current will be 1/sqrt(3) of the line current. If three phase CTs are connected in Delta, their secondary current will be sqrt(3) higher than the CT ratio implies by the line current.


How do you start a three phase motor to a single phase power supply?

You don't. A three phase motor will not start unless it is connected to a three phase supply.


Theory for brake test on three phase induction motor?

why three phase induction motor is delta connected


Why is there no neutral point for delta?

There is no neutral in a delta connection, because that is the definition of delta, a power configuration where current flows from phase hot to phase hot. The loads are A-B, B-C, and C-A. Contrast this with star, where there is a neutral, and the loads are A-N, B-N, and C-N.


How do you determine a 3 phase motor and each winding?

To see if the motor is three phase or single phase look at the motor's nameplate. There it will tell you what the voltage needs to be and what system phase the motor needs to be connected to operate properly.


Can a 3 phase motor be converted into a single phase motor?

A three-phase motor will not start if one or two phases aren't connected. If while running one or two phases "drop out", it will continue to run for awhile, but will eventually burn out, unless connected to a motor saver.


Can a single phase motor be wired to a three phase soft start?

No, a single phase motor cannot be directly connected to a three phase soft start. A single phase motor requires a single phase power supply, while a three phase soft start is designed for three phase motors. Using the correct soft start for the motor type is essential for proper operation and protection of the equipment.


How do you wire 3 phase power to 1 phase power diagram?

In an emergency and for a short period of time you can single phase a three phase motor but the motor will be loud, have terrible power characteristics and depending upon the use will burn up rather quickly. You should never try to run this in other than a life threatening emergency situation, the motors are not designed for it. Normally you don't. <<>> A three phase motor will not start on single phase. If the motor was started on three phase and loses a phase, it will stay running at a lower percentage of efficiency. Now a days the motor protection will not let a three phase motor run in a single phasing condition. All three phase legs of the motor are monitored and in a single phase condition the other two legs of the motor draw a higher current. This higher current is sensed by the motor's overload heaters in the motor's contactor and take the motor off line by opening the motor contactor. Now to the question, any two legs of a three phase system in electrical terms is known as single phase. As long as the three phase voltage matches the voltage needed in the single phase power diagram it can be connected to operate single phase equipment.


How many percent will be the starting current for motor?

Motor starting current is typically 5-7 times the rated current of the motor. (For three phase induction motors)


Why neutral not conect in 3phase motor?

A 3 phase motor does not require a neutral conductor because the impedances that make up the stator coils are of equal magnitude and it is what is known as a balanced 3 phase load. If the loads of a wye connected 3 phase system were unbalanced, i.e. the load currents in each of the 3 phases are different, then the unbalanced currents would require a return path to the service transformer via a neutral conductor. The neutral conductor is the transformer centre tap and is usually earthed locally. ANOTHER ANSWER The impedance of each phase winding of a three phase motor is identical (we call it a 'balanced load'). For a star (wye) connected motor, the phasor sum of three identical phase currents is zero, so no current will flow through a neutral, so a neutral isn't required. For a delta-connected motor, there is no provision for a neutral.


Condition of three phase in which there is no need of neutral?

A delta-connected system is described as being a three-phase, three-wire, system, and doesn't have a neutral. But a balanced star (wye) connected load (e.g. a three-phase induction motor) doesn't actually require a neutral.