Wiki User
β 15y agoAssuming being fed by c32 breaker for start load minimum cable size SWA is 70mm which will go to 456 meters
Wiki User
β 15y agoFor a 3KW motor with a 350-meter run and 240V supply voltage, you would typically need a cable size of around 16mmΒ² for proper voltage drop considerations and to prevent overheating. It's recommended to consult with a qualified electrician or use a voltage drop calculator to determine the exact cable size needed for your specific installation.
For a 37 kW induction motor, a cable size of approximately 10 AWG (American Wire Gauge) would be suitable for typical installations. However, the specific cable size required would depend on factors such as the length of the cable run, ambient temperature, and voltage drop considerations. It is recommended to consult with a qualified electrician to determine the appropriate cable size for your specific application.
For a 7.5 hp motor operating at 240V, you would typically use a 14-gauge wire and a 40 amp breaker. However, it is best to consult the motor's specifications and the National Electrical Code to determine the exact wire size and breaker needed for your specific setup.
For a 26kW, 415V induction motor with a 50m cable run, you would typically need a cable size of at least 6mm^2 to ensure proper voltage drop and current carrying capacity. However, it is always recommended to consult local electrical codes and standards or a licensed electrician to determine the exact cable size needed for your specific installation.
i have 200 hp motor what i need cable size in 100 feet distance
To calculate the cable size for a 30-meter run, you need to consider the current rating of the circuit, voltage drop limits, and the type of cable insulation. Use a cable sizing calculator or consult a professional electrician to determine the appropriate cable size to ensure safety and efficiency of the electrical installation.
16 mm square
Sir, what is the cable size for 1.5kw 3phase induction motor 400v?
If I consider power factor is 0.85 & motor efficiency is 95% then you have required 4 sq mm wire which is able allow passing 25.47 A current trough it.
How to calculate a cable size of 3kw motor
Cables are rated are by the max current they can supply. To work out the current load you need to divide the Watts by the Voltage (which is either 120 or 240 depending on where you are). In the UK: 4kW/240V = 4000/240 = 16Amps, so the cable would probably be rated for 20 amps. In the US the current is 32Amps, so the cable would probably be rated for 50 amps.
For a 37 kW induction motor, a cable size of approximately 10 AWG (American Wire Gauge) would be suitable for typical installations. However, the specific cable size required would depend on factors such as the length of the cable run, ambient temperature, and voltage drop considerations. It is recommended to consult with a qualified electrician to determine the appropriate cable size for your specific application.
Need to know what the voltage of the motor is.
you need the current of motor or the KW/HP rating
take the full load current 1.732*415*I*0.85*efficiency=115*1000 => I? Depending on the value of the full load current and designed and ambient temperatures of the selected category of the cables, and voltage drop per unit length, you can determine the cable size
# 2-awg
35 KVA generator using for load 100 meter length which cable need to used
To calculate voltage drop to size the wire, a voltage must be stated.