answersLogoWhite

0


Want this question answered?

Be notified when an answer is posted

Add your answer:

Earn +20 pts
Q: What does the magnetic trip of a circuit breaker indicate?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

How much current flows through circuit breaker trip coil?

The current flowing through a circuit breaker trip coil is typically very low, on the order of milliamps. This current is used to activate the trip mechanism, causing the circuit breaker to open and disconnect the circuit in the event of an overcurrent or short circuit. The exact amount of current can vary depending on the specific design and rating of the circuit breaker.


What is a Instantaneous trip breaker?

An instantaneous trip breaker is a type of circuit breaker that trips immediately when a fault is detected, without any delay. It provides quick protection to the electrical system by cutting off the circuit as soon as an overcurrent or short circuit occurs.


When a shunt trip breaker trips does the voltage remain on?

No, when a shunt trip breaker trips, it opens the circuit and disconnects the voltage supply to the protected circuit.


What does the trip free characteristic of a circuit breaker mean?

A trip free circuit breaker is one that will disconnect a circuit even if the manual switch is held at the "on" position. It is a safety feature to prevent a circuit breaker being disabled either deliberately or accidentally.


If a shunt trip occurs does breaker go to off or trip position?

When a shunt trip occurs, the breaker typically goes to the "trip" position, which indicates that the circuit has been interrupted and the contacts are open. This allows for quick identification of the issue and isolation of the circuit for safety reasons.

Related questions

How much current flows through circuit breaker trip coil?

The current flowing through a circuit breaker trip coil is typically very low, on the order of milliamps. This current is used to activate the trip mechanism, causing the circuit breaker to open and disconnect the circuit in the event of an overcurrent or short circuit. The exact amount of current can vary depending on the specific design and rating of the circuit breaker.


What are the devices contain in a circuit breaker?

The devices contained in a circuit breaker consist of a bi metal strip for over load protection and a small wrap of wire in the form of a coil for magnetic short circuit trip.


How does a circuit breaker know that the voltage is high or low and trip off?

A circuit breaker doesn't respond to excessive voltages, but to excessive currents (overcurrents). A miniature circuit breaker, the type you have at home, has a bimetallic strip and a coil, either of which will initiate a trip in response to excessive temperature (overload currents) or excessive magnetic flux density (short-circuit currents).


What is the difference between thermal magnetic release circuit breaker microprocessor based release circuit beraker?

As far my knowledge goes the only difference i found in a thermal magnetic relase & microprocessor based was in a microprocessor based Circuit breaker we have a additional protection i.e. for Earth fault. Aparts that the range of fault setting in a microprocessor based circuit breaker is more than in a thermal magnetic trip unit.


What is the purpose of the flux shifter in a low voltage circuit breaker?

A trip rod on the circuit breaker is spring loaded and held by a permanent magnet in the "armed" position; the flux shifter, when energized due to an overcurrent event, creates a magnetic field opposite the permanent magnet field....this neutralizes the magnetic field, releasing the trip rod.


What is a Instantaneous trip breaker?

An instantaneous trip breaker is a type of circuit breaker that trips immediately when a fault is detected, without any delay. It provides quick protection to the electrical system by cutting off the circuit as soon as an overcurrent or short circuit occurs.


What are the breaker ampere trip ratings?

The ampere frame rating for a circuit breaker designates how the circuit breaker should be configured. It also states the trip unit of the amp.


What is the function of an LBB relay?

A local breaker backup relay is used to check the operation of distribution circuit breakers and to trip the feeder circuit breaker if the distribution circuit breaker fails to trip on an overload.


When a shunt trip breaker trips does the voltage remain on?

No, when a shunt trip breaker trips, it opens the circuit and disconnects the voltage supply to the protected circuit.


What is a non auto circuit breaker?

A non-auto circuit breaker is a circuit breaker with the trip element removed. Basically, it is a modified circuit breaker that is now a disconnect switch (glorified disconnect switch).


What does the trip free characteristic of a circuit breaker mean?

A trip free circuit breaker is one that will disconnect a circuit even if the manual switch is held at the "on" position. It is a safety feature to prevent a circuit breaker being disabled either deliberately or accidentally.


What is the difference between MCB and MCCB?

MCB (Miniature Circuit Breaker)-rated current not more than 100 A. Trip characteristics normally not adjustable. Thermal or thermal-magnetic operation. Breakers illustrated above are in this category.MCCB (Molded Case Circuit Breaker)-rated current up to 2500 A. Thermal or thermal-magnetic operation. Trip current may be adjustable in larger ratings. MCB (Miniature Circuit Breaker)-rated current not more than 100 A. Trip characteristics normally not adjustable. Thermal or thermal-magnetic operation. Breakers illustrated above are in this category.MCCB (Molded Case Circuit Breaker)-rated current up to 2500 A. Thermal or thermal-magnetic operation. Trip current may be adjustable in larger ratings.from Manu anand