Best Answer

Branch circuit loading In Canada the CEC states that there shall be not more than 12 outlets on any 2-wire branch circuit. These outlets shall be considered to be rated at not less than 1 amp per outlet

Where the connected load is known, the number of outlets shall be permitted to exceed 12, provided that the load current does not exceed 80% of the rating of the over current device protecting the circuit. For example on a 15 amp breaker, 15 x 80% = 12 amps, hence the standard of 12 outlets on any 2-wire branch circuit.


On a 20 amp breaker, 20 x 80% = 16 amps. So from a 20 amp breaker this allows 16 outlets on a 2-wire branch circuit as long as the outlets are not considered to be rated at less than 1 amp per outlet.


The definition of an outlet is a point in the wiring installation at which current is taken to supply utilisation equipment. What this means is that if a light switch and a fixture outlet were on the same 2-wire branch circuit they would be subtracted from the maximum count of 12 receptacle outlets on the circuit which would leave 10.


If the light fixture draws 3 amps plus the switch outlet, then the total circuit outlet count would be reduced to 8 receptacle outlets (12 – 3 – 1 = 8).


On a standard specification home most electricians will wire one circuit per room, the outlet count usually never reaches the maximum of 12 outlets.

User Avatar

Wiki User

βˆ™ 8y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many oulets in a 15 amp breaker circuit?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

Can you replace a 20 amp circuit breaker with a 25 amp circuit breaker?

It is not recommended to replace a 20 amp circuit breaker with a 25 amp one. Circuit breakers are designed to protect the wiring and equipment from overheating and potential fires. Using a breaker with a higher rating than the wiring can handle increases the risk of overheating and could lead to a fire hazard. It is important to match the circuit breaker size to the wiring and equipment it is protecting.


Can a circuit breaker be tripped by using 20 amp sockets instead of 15 amp sockets?

A circuit breaker protects the wires that the devices are connected to. If the devices that are connected to the circuit are 20 amps the wire size should be #12 wire fed from a 20 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. If the devices that are connected to the circuit are15 amps the wire size should be #14 wire fed from a15 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. Putting 20 amp sockets on this 15 amp circuit will work but the circuit is limited to the amount of load that can be plugged in. You will not get the full capacity of the 20 socket because the breaker will trip at 15 amps.


Does square D make a circuit breaker with a 15 amp and 20 amp breaker in the same breaker?

No tandem breakers are of the same value.


What circuit is a microwave?

A dedicated 20 Amp circuit wired with 12/2 wiring an a 20 amp breaker.


Is a 40 amp circuit breaker ok for a 30 amp air conditioner?

No, it is not recommended to have a circuit breaker with a higher amperage rating than the device it is protecting. In this case, you should use a 30 amp circuit breaker for a 30 amp air conditioner to ensure proper protection from overcurrent.

Related questions

New shop 20 amp circuit 32 amp fixture how many fixtures can be put on circuit?

A 32 amp fixture can not be fed from a 20 amp breaker as the breaker will trip every time.


How many ampacity rating do a circuit breaker need for the general purpose circuit?

Usually a 15 or 20 amp breaker is sufficient


How do you turn a 30 amp circuit into a 15 amp cicuit?

Replace the 30 Amp Breaker with a 15 Amp breaker.


Can you replace a 20 amp circuit breaker with a 25 amp circuit breaker?

It is not recommended to replace a 20 amp circuit breaker with a 25 amp one. Circuit breakers are designed to protect the wiring and equipment from overheating and potential fires. Using a breaker with a higher rating than the wiring can handle increases the risk of overheating and could lead to a fire hazard. It is important to match the circuit breaker size to the wiring and equipment it is protecting.


Can you upgrade a 15 Amps circuit breaker for a 40 Amp for a 8.5 Watt shower?

Not unless you change the wiring for that circuit. The breaker protects the wiring and if you install a 40 amp breaker on a 15 amp wire circuit you will have a fire in your home.


How many 1.2 amp lights can a 20 amp breaker hold?

No more than 13 maximum on a 20 amp circuit.


What size amp circuit breaker should be used for a pool light?

The pool light is usually on a 15 amp circuit. The breaker feeding this circuit must have a GFCI rating.


How many amp circuit breaker for 3 hp 230 volt motor?

16A


Can a circuit breaker be tripped by using 20 amp sockets instead of 15 amp sockets?

A circuit breaker protects the wires that the devices are connected to. If the devices that are connected to the circuit are 20 amps the wire size should be #12 wire fed from a 20 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. If the devices that are connected to the circuit are15 amps the wire size should be #14 wire fed from a15 amp breaker. This breaker should not trip unless the circuit is overloaded or a fault occurs on the circuit. Putting 20 amp sockets on this 15 amp circuit will work but the circuit is limited to the amount of load that can be plugged in. You will not get the full capacity of the 20 socket because the breaker will trip at 15 amps.


Does square D make a circuit breaker with a 15 amp and 20 amp breaker in the same breaker?

No tandem breakers are of the same value.


Can you use a fifty amp circuit breaker for a forty amp appliance?

Yes.


What size circuit breaker should be used for dishwasher and disposal?

A 15 amp dedicated circuit breaker should be used for the dishwasher. The disposal can be wired to the general kitchen 15 amp circuit.