To calculate the amperage for a 10kW heater on a 3-phase 220V system, use the formula: Amps = (kW x 1000) / (√3 x Volts). So, Amps = (10 x 1000) / (√3 x 220) = 26.18 amps per phase. Therefore, the total current drawn by the heater is 26.18 amps per phase multiplied by 3, which equals approximately 78.54 amps.
To calculate the current draw, use the formula: Current (A) = Power (W) / (Voltage (V) * √3). Plugging in the values, we get Current = 30000W / (208V * √3) ≈ 78.7A. So, a 30KW strip heater operating at 208 volts 3-phase would draw approximately 78.7 amps.
To calculate the amperage, you can use the formula: Amps = (kW × 1000) / (√3 × Volts). Plugging in the values, we get: Amps = (45 × 1000) / (√3 × 208) ≈ 131.1 amps. So, the hot water heater would draw approximately 131.1 amps.
To calculate the amperage, you can use the formula: Amps = Watts / Volts. In this case, a 400-watt heater cartridge at 240 volts would draw 1.67 amps.
A block heater typically draws around 6 to 10 amps of current. It may vary depending on the wattage of the heater and the voltage of the electrical system it is connected to.
To answer this question the voltage of the heater must be given. I = W/E.
For a single phase circuit, the equation you are looking for is I = W/E. Amps = Watts/Volts.
To calculate the amperage for a 10kW heater on a 3-phase 220V system, use the formula: Amps = (kW x 1000) / (√3 x Volts). So, Amps = (10 x 1000) / (√3 x 220) = 26.18 amps per phase. Therefore, the total current drawn by the heater is 26.18 amps per phase multiplied by 3, which equals approximately 78.54 amps.
To calculate the current draw, use the formula: Current (A) = Power (W) / (Voltage (V) * √3). Plugging in the values, we get Current = 30000W / (208V * √3) ≈ 78.7A. So, a 30KW strip heater operating at 208 volts 3-phase would draw approximately 78.7 amps.
To calculate the amperage, you can use the formula: Amps = (kW × 1000) / (√3 × Volts). Plugging in the values, we get: Amps = (45 × 1000) / (√3 × 208) ≈ 131.1 amps. So, the hot water heater would draw approximately 131.1 amps.
To calculate the amperage, you can use the formula: Amps = Watts / Volts. In this case, a 400-watt heater cartridge at 240 volts would draw 1.67 amps.
A block heater typically draws around 6 to 10 amps of current. It may vary depending on the wattage of the heater and the voltage of the electrical system it is connected to.
30
100 KW divided by 415 volts is 241 amperes. Power = voltage times current, so current = power divided by voltage.
For a 1hp 3-phase motor, the current draw will depend on the voltage supply. Typically, at 230V, a 1hp 3-phase motor will draw around 3.6 amps. However, this value may vary based on the motor efficiency and power factor.
Assuming the power factor is 1, a 10 hp motor operating at 600 volts in a three-phase system would draw approximately 13.33 amps.
9000 BTU/hour is equivalent to 2300 watts so the heater will draw 10 amps on 230 volts.