answersLogoWhite

0


Best Answer
Answer for USA, Canada and countries running a 60 Hertz supply service.

The 277 volt heater can be wired to a single pole breaker in a 3 phase 4 wire 480 volt distribution panel. The breaker should be sized to the amperage draw of the heater. 277 volts is the star point (wye) voltage of a 480 3 phase system. 480 / 1.73 = 277 volts. The third answer is not correct, two phase legs of a 480 volt system will give you 480 volts. It is the phase leg to ground (neutral) that gives you the 277 volts.

<<>>

A 277 Volt heater or device may not be wired to a 480 Volt circuit or box. A 277 Volt device may only be wired to a circuit rated for 277V/480V equipment.

2 legs of 480 volts will give you 277. But since you don't know the answer you probably shouldn't be doing it! Please don't kill yourself, hire a licensed electrician.

Before you do any work yourself,

on electrical circuits, equipment or appliances,

always use a test meter to ensure the circuit is, in fact, de-energized

IF YOU ARE NOT REALLY SURE YOU CAN DO THIS JOB

SAFELY AND COMPETENTLY

REFER THIS WORK TO QUALIFIED PROFESSIONALS.

User Avatar

Wiki User

13y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

5mo ago

To wire a 277 volt heater from a 480 volt box, you will need to use a step-down transformer to reduce the voltage from 480 volts to 277 volts before connecting the heater. Make sure to properly size the transformer to handle the load of the heater and follow all local electrical codes and regulations when performing the wiring. It is recommended to consult with a licensed electrician to ensure the wiring is done safely and correctly.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How do you wire a 277 volt heater from 480 volt box?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

What is the benefits of using 277 volt electrical equipment?

with 3 phase lighting you do not have to use as large of wire and can use one neutral for every 3 current carrying conductors so it cut down on material costs ( as voltage increases current decreases) &lt;&lt;&gt;&gt; The voltage 277 is the star-point voltage of a 480 volt three phase system. By using a 480 volt wye system you have the dual ability of running 480 volt three phase equipment along with 277 volt lighting. The side advantage is the ability of using the phase voltage to ground (neutral) 480 / 1.73 = 277 volts for general lighting of the building the 480 volt equipment is located in.


Is 277 volt one hot wire?

No, 277 volts is the line to neutral of a 480 volt wye three phase system. L1- N, L2 - N and L3 - N will give you 277 volts. L1 to L2. L2 to L3 and L3 to L1 will give you 480 volts.


Can a 277 unit heater be supplied with 240 volts?

No, a 277-volt heater cannot be safely operated with a 240-volt power supply. Matching the correct voltage is essential for the safe operation of electrical devices. Using a lower voltage than the device is rated for can lead to insufficient performance and potential damage.


What color should a H2 Conductor on 480 volt transformer should be marked?

The conductor for H2 connection on a 480 volt wire transformer should be marked:


How do you convert 277v to 120v for an outlet?

i think you just have to change the breaker from a 277 to a 120. 277 breakers are usually a 2 pole breaker and 120 is a single pole breaker. NO. 277v is not two poles, it is one pole, one single pole breaker in a 480 volt 3 phase system (typically). If you want 120 volts from a 277 volt source you need a step down transformer 277 volt to 120 volt , or 480/277 to 120/208 .

Related questions

Do you need a neutral to install 480 volts 3 phase heater?

If the heater is rated as a 3 phase 480 volt heater then a neutral is not needed. If the voltage stated is 277 volts three phase then a neutral is needed.


Wiring diagram to convert a 3 phase 480 volt generator to 277 volt?

You should not need a wiring diagram. If the generator has a star point (wye) connection then the phase voltage to ground (star point) is 277 volts. 480/1.73 = 277.


What is the benefits of using 277 volt electrical equipment?

with 3 phase lighting you do not have to use as large of wire and can use one neutral for every 3 current carrying conductors so it cut down on material costs ( as voltage increases current decreases) &lt;&lt;&gt;&gt; The voltage 277 is the star-point voltage of a 480 volt three phase system. By using a 480 volt wye system you have the dual ability of running 480 volt three phase equipment along with 277 volt lighting. The side advantage is the ability of using the phase voltage to ground (neutral) 480 / 1.73 = 277 volts for general lighting of the building the 480 volt equipment is located in.


What voltage reading would you get from a 277 480 volt system?

From a three phase four wire distribution system the voltages would be as follows. From L1 to N - 277 volts. From L2 to N - 277 volts. From L3 to N - 277 volts. From L1 to L2 - 480 volts. From L2 to L3 - 480 volts. From L3 to L1 -480 volts.


Is 277 volt one hot wire?

No, 277 volts is the line to neutral of a 480 volt wye three phase system. L1- N, L2 - N and L3 - N will give you 277 volts. L1 to L2. L2 to L3 and L3 to L1 will give you 480 volts.


What is a 277 volt fluorescent fixture?

A 277 volt lighting fixture is one that is usually used in an industrial application. The reason for this is the voltage rating. A voltage potential of 277 volts is the voltage to neutral (ground) of a three phase four wire 480 volt distribution system. 480 volts / 1.73 = 277 volts. Rather than having to add a transformer to the system to provide 120 volts for lighting, manufactures produced a ballast for fluorescent fixtures that operates on the 227 volt potential.


How do you wire a 277 to 120 volt transformer?

The voltage 277 volts is a three phase line to neutral voltage of a 480 volt system. What is needed for the protection of the transformer is a two pole breaker from the 480 volt CDP (Central Distribution Panel). The breaker will be sized to the KVA of the transformer. The wire will be sized to the breaker plus 25%. The electrical code requires that on motor and transformer feeders, they be sized to 125% of the total current capacity of the equipment.


Can a 277 unit heater be supplied with 240 volts?

No, a 277-volt heater cannot be safely operated with a 240-volt power supply. Matching the correct voltage is essential for the safe operation of electrical devices. Using a lower voltage than the device is rated for can lead to insufficient performance and potential damage.


Can you get 120 volts from a 480 volts 3 phase Y generator?

NO, the 480 Volts Y -- is 4 wire system, with three wires which are hot legs @ 480 volts between each three hot legs. A mid tap is a neutral leg (ground) the white wire. Which gives 277 volts between it and any of the three hot legs. so a 4wire 480 volt Y system. Gives 480 /277 volts.


How to wire 277 volt lighting?

A voltage of 277 is the line to neutral voltage of a 480 volt wye three phase system. L1- N, L2 - N and L3 - N will give you 277 volts. L1 to L2. L2 to L3 and L3 to L1 will give you 480 volts. Wiring of three phase equipment should be in the domain of qualified journeyman electrician or apprentices under the supervision of a qualified journeyman electrician.


Can you run single phase 230 from one side of 480 volt 3 phase?

No, you will not obtain 230 volts. From a wye connected three phase 480 volt supply, 277 volts can be obtained from one phase leg and the neutral on the wye connection. 480 volts/1.73 (sq. root of 3) = 277 volts.


What is the voltage of a 3 phase 4 wire 277 volt lighting circuit?

The voltage of 277 volts is the wye of a three phase 480 volt system. Just as the voltage of 347 is the wye voltage of a three phase 600 volt system. To obtain these voltages for any three phase system, take the three phase voltage and divide it by 1.73. 480/1.73 = 277 volts, 600/1.73 = 347 volts.