answersLogoWhite

0


Best Answer

The formula is that kW^2 + kVAR^2 equals kVA^2 or if you prefer, the kW and the kVAR are the two sides of a right angled triangle and the kVA is the hypotenuse.

So here you have a 3-4-5 triangle times 140, in other words 420-560-700, and the kVAR is 420.

User Avatar

Wiki User

11y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

5mo ago

To calculate kVAR, first find the apparent power (S) using the formula: S = √(P^2 + Q^2), where P is the real power (in kW) and Q is the reactive power (in kVAR). Given P = 560 kW and kVA = 700, kVA = √(P^2 + Q^2) implies 700 = √(560^2 + Q^2). Solve for Q to find the reactive power kVAR.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How calculate kvar if p is 560 kw and kva is 700?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How do you calculate KVAR from micro farads?

kvar = kva*sin@


How do you calculate kvar from micro-farad?

kvar = kva*sin@


How calculate kvar?

kvar can be calculated as follows the a product KVA andt the sine of the angle between the KVA and KW.


How does kvar work?

kvar can be calculated as follows the a product KVA andt the sine of the angle between the KVA and KW.


What is the KVAR if kva is 1750 and kw is 1225?

To find KVAR, we can use the formula: KVAR^2 = KVA^2 - KW^2. Plug in the values given: KVAR^2 = 1750^2 - 1225^2. Calculating this gives KVAR = 1050.


Convert 800kvar to kw?

The same way, as you convert Appels to Carrots ........... There is a formula: KVAr = KVA / KW or cos=KW/KVA > Yes, we are treating KW, KVA, & KVAr as the 3 sides in a 90 deg TRIANGLE ! KW= vertical katede KVAr = horizontal katede KVA = hypotenuse


What is Kvr?

kV is kilovolts, kW is kilowatts, kVA is kilovolt amps and kVAR is kilovolt-amps reactive. A common formula is kVA-squared = kW-squared + kVAR-squared.


How many kVA equal kvar?

For normal power factors (pf=80%), you have 0.8 kW for every kva. In general however, kW = pf x kVA. Where pf is the power factor, it is the cosine of the angular difference between the voltage and the current of a circuit in alternating current circuits.


What is the Formula to calculate KVAR?

{| |- | capacitance of the capacitor is mentioned in KVAR. Formula : KVAR = KW*tan@ FOR tan@, First note the power factor & KW without connecting capacitor. The noted power factor is in cos@.Convert the cos@ value in tan@. for ex. If power factor is 0.6, KW = 200 cos@ = 0.6 cos-1 (0.6) = 53.1 tan (53.1) = 1.333 200*1.333 = 266.6 KVAR if you use 266 KVAR capacitor, Then the power factor improves to unity (1.000). |}


Why alternators are measured in Kva but not in KW?

Depending upon the connected load ( R, RL, RC or RLC) with a transformer, the power goes ou from a transformer may be of two types: 1. Active Power; measured in kW 2. Reactive Power; measured in kVAR If the rating will be in kW, then kVAR rating would not be accounted but if the rating is in kVA then it is possible for us to calculate the total active and reactive current as well as the powers, at a particular system voltage!


What happen if generator run on leading power factor?

When the power factor is leading, the capacitive kVAr is more than the Inductive kVAr and this still has to be supplied by the source. As kVA is the vector sum of kW and kVAr, still for the given kW, you have to produce more kVA. Alternately, for the given kVA, you can only convert partially into useful work. Secondary effects are voltage boost in the system, availability of stored energy to feed the fault in case of a fault, increase in the asymmetrical component of fault current, increasing thus the peak value of the fault current, etc.


How many KW is in 150 KVA?

To convert KVA to KW, you need to know the power factor of the system. Assuming a power factor of 0.8 (common for many systems), the formula for converting KVA to KW is KW = KVA * power factor. With a KVA of 150 and a power factor of 0.8, the KW would be 150 * 0.8 = 120 KW.