answersLogoWhite

0


Best Answer

Electromechanical relays (not just earth fault relays) need to be calibrated to insure they are operating in the expected way. A simple overcurrent ground relay will have a tap setting, and a time dial setting. These are chosen by a protection engineer to coordinate with other ground protection devices upstream and downstream. If the relay is not calibrated correctly, the relay will not operate at the expected tap value, or may operate slower / faster due to the time dial calibration being different than expected. This can cause over tripping, removing more equipment from the power system than is necessary to clear a fault.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Why you need calibration for earth fault relays?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

Why ngt or ngr used in transformer?

Criteria-in order to protect the stator core from damage during internal earth fault it is necessary to limit the stator earth fault current al low as possible.may be upto 10amp for generator. Basis for selection of ngtr- if generator is connected to the system through generator transformer then generator can be treated as an isolated system which is not influenced by the distribution earthing system. In this case you can select earth fault current as low as possible, but if we use ngr then in order to limit the low earth fault current size of the ngr will be increased.due to big size of ngr we required more space & also its too costly. V = ir means if v constant i is inversely proportional to r exp:-to limit 10amp current , v =11kv/root 3 r = 11/root 3/10*1000=635.10 ohm ( very high value) for overcome on this, general practice to use a ngtr so that we can limit low earth current without any extra cost. Exp:- ngtr 11/240v to limit 10amp current current reflect on secondary side of ngtr will be = (11000/root 3/240)*10=264.6 amp. Resistor value on secondary side r =240/264.6 =0.9 ohm ( approximately) which is much lower than 635.10 ohm. Basis for selection of ngr- if generator is directly connected to the system then we can not limit the earth fault current up to 10 amp. We have to select the earth fault current value above the residual capacitive charging current of system.also we need to check the possibility of relay setting operation with ct ratio. For exmp- if ct ratio is 2000/1amp & earth fault limit current is 100amp relay selected with 10 % setting. Then that relay will see only 200amp earth fault current it will not see 100amp current. Also we can not keep generator solidly grounded because of high earth fault current stator can damage same will happen with ht motor if it is connected to this system. So for this case we need to select the ngr with proper earth fault current


Do you need a ground fault breaker for your hot tub?

Yes, the electrical code requires a ground fault breaker for your hot tub.


Do multimeters need calibration?

All test equipment has to be calibrated. It is calibrated when it comes from the manufacturer but depending on how much the test equipment is used recalibration is usually recommended.


What are the applications of solid state relays?

Solid state relays have no moving parts and do not spark, as there are no contacts. They are more expensive and need to be matched closely to the voltages and currents used. They are best used where sparking may be an issue (explosive gas atmospheres) or where longevity is required.


What is the advantage and disadvantage of open delta bank transformer?

A disadvantage with Open Delta is there are no phase-ground voltage measurements, which is only a disadvantage if directional relaying or distance relaying is needed. Some directional and voltage based ground fault detection relays don't work without the phase to ground input. Since most industrial systems MV are high resistance grounded and ground fault protection is provided by overcurrent, there isn't a need for the phase-ground measurements.Why will the directional or distance relaying not work in this case?5. Most directional and distance relays need a voltage to ground reference to compare with the phase current nfr groudn faults. Some can use a zero sequence polarising current from CT's on the neutral of the transformer, but most need phase-neutral voltages for accurate calculation of fault direction and distance.The relay needs to see a zero sequence voltage to compare to the zero sequence current to find out which direction the current is flowing.Precise Phase-ground voltages are needed for this type of calculation, whether it is done digitally or with analog circuits or windings, coils and phae shifting circuits.The voltages provided by the Open Delta do not have enough zero sequence component.

Related questions

Why we are using inductive loads for calibration?

You need to specify the kind of calibration you are asking, to get the right answer


Where can I rent calibration equipment in Raleigh, NC?

you can rent calibration equipment in Raleigh, NC. ONly thing you need to search in the google that rental for Calibration Equipment in Raleigh, NC


How do you adjust the calibration of pocket scale?

To adjust the calibration of a pocket scale, you will typically need a calibration weight that matches the capacity of your scale. Place the calibration weight on the scale and follow the instructions in the user manual to calibrate it by adjusting the calibration setting until the scale displays the correct weight.


Why percentage differential relays do not normally need to be coordinated with the action of any other relay?

Differential relays should only operate for faults within the zone of protection, so there is no coordination issue. The reason to coordinate relays is for backup protection (a relay at a remote substation sees faults that should be cleared by another relay, for example). A differential will not see this fault, since it is external to it's zone of protection.


Where is relays located on 1991 s10?

There are several relays on that vehicle. We need to know which one you are looking for.


Does a humidity sensor need calibrating?

Yes, a humidity sensor may need calibration to ensure accurate readings over time. Calibration involves adjusting the sensor to a known reference or standard to minimize errors in humidity measurement. Calibration is essential for maintaining the sensor's accuracy and reliability.


Do you need additional relays for a keyless entry system if you have power door locks?

You should already have relays if you have power doorlocks


When would you carry out the calibration procedures for the experiment?

Calibration procedures should be carried out at the beginning of the experiment to ensure accuracy and reliability of the measurements. Additionally, calibration may need to be performed periodically throughout the experiment to account for any changes or drift in the equipment's accuracy.


What the face on a card in Kinect adventures for?

This is the kinect calibration card. If you need to calibrate your kinect, grab your remote and go to the calibration center. You line the card up with on screen glasses. Don't throw it away in case you get in trouble and need it.


What do I need to weigh 100 grams in order to calibrate my scales?

You would need an object that is exactly 100 grams in weight, such as a calibration weight. Place this object on the scales and adjust the calibration settings until it reads 100 grams.


Where is the turn signal relay located at on a Ford F650?

it is located under the radio kinda above the floor heater duct tube ,,relays face to the passengers side ... remember the relays need to be for turn signals NOT relays for lighting!!!! turn relays are blue !!!!


What are the properties of earth electrodes?

Earth electrodes have low resistance to earth, provide a stable connection to the ground, and can dissipate fault currents safely. They also need to have good corrosion resistance to maintain their effectiveness over time.