In a perfect world the insulation factor would be infinity. This does not happen due to contamination of the insulation, water vapour or water in a conduit system are a couple of scenarios that will bring the resistance reading to a lower level. A megohm meter (megger) is the test equipment that is used to measure the insulation factor of conductors. On a 600 volt system the load can be energized with a reading as low as 500k. Engineer projects require a minimum of 5 megohm readings. Systems that have been in service for a long time usually ring in at 1 to 2 megohms.
An open circuit essentially has an infinite resistance. It is shown on digital multimeter as OL. (Open Line) A short circuit should read zero, or nearly zero, depending on the accuracy of the meter.
Resistance is directly proportional to the resistivityand length of a material, and inversely-proportional to its cross-sectional area. It should also be noted that its resistivity is affected by temperature, so temperature indirectly affects resistance.
insulation resistance can be measured by means of megger, with built in d.c generator. It is measured between the conductor and the earth. earth resistance can be measured by means of earth resistance tester. For good effective earthing, th earth resistance should be of order 0.5 ohm
Because ordinary ohmmeters are calibrated to measure a range of resistance values that are significantly lower than the resistance of insulation. It should also be realised that we usually test insulation resistance while subjecting the insulation to a high electric field, which a normal ohmmeter is incapable of producing.
To test for resistance in a circuit, the circuit should be de-energized.
A megger is an electrical instrument that is used to measure the resistance of insulation by applying a DC voltage to the conductor. One lead is connected to the conductor and the other lead is connected to ground. Safe insulation reading to ground should be above 2,000,000 ohms or 2 megs.
The maximum insulation resistance for a 230 volt 50Hz domestic circuit should be at least 1 Megaohm (1,000,000 ohms) per volt of applied voltage, which would be 230 Megaohms. This is based on the general rule of thumb that insulation resistance should be at least 1 Megaohm per volt for safe operation. Insufficient insulation resistance could result in electrical leakage, shocks, or fires in the circuit.
A short circuit is a direct connection between two points in a circuit that have different voltages, causing excess current flow. This can happen due to damaged insulation or faulty wiring. Short circuits are dangerous because they can cause overheating, fires, and damage to electronic devices.
Question should be clear For Thermal insulation,Electrical insulation,energy insulation vision insulation.
Insulation resistance.
Branch circuits are protected by the circuit breaker found in the electrical panel. Each circuit should have its one breaker. The breaker should be rated to protect the insulation of the wire, so you can determine the breaker size based on the circuit conductor size Example #14-2 should be protected by a 15 amp breaker
Insulation resistance should be approximately one megohm for each 1,000 volts of operating voltage, with a minimum value of one megohm. For example, a motor rated at 2,400 volts should have a minimum insulation resistance of 2.4 megohms.
No. There should be substantial resistance only where the circuit design needs it and wants it, and as little as possible everywhere else in the circuit.
Values of insulation resistance vary according to the type of insulators and the size of the conducting material inside the insulators, for instance insulation resistance of wires or cables are determined according to type of insulation PVC-PE-XLPE-..... etc and the size of the conductor, and the standard which the wires or cables are designed upon. For example BS 5308 standard states that cables of conductors 0.5, 1, and 1.5 with PVC insulation should have a minimum insulation resistance of 25 Mohm.km . but cables with PE insulation should have a minimum insulation resistance of 5 Gohm.km ...... Now you may realize the difference in IR values. I hope I manage to make it clear image for the answer.
An open circuit essentially has an infinite resistance. It is shown on digital multimeter as OL. (Open Line) A short circuit should read zero, or nearly zero, depending on the accuracy of the meter.
Resistance is directly proportional to the resistivityand length of a material, and inversely-proportional to its cross-sectional area. It should also be noted that its resistivity is affected by temperature, so temperature indirectly affects resistance.
By Megger testing (meggering) of the motor any one can measure the IR of the motor. MEGGER is a device used to measure IR. Analog Megger device may generate 500 volts..it gives coil to coil or coil to body IR value...it should not be less than 2 Mega ohm, generally it should be or kept more than 5 mega ohm...thanks ...DEEPAK RAJPUT