It will not work at all.
My first thought is this is probably a corner grounded delta system, but I'm confused by your voltages. If this was a 460v (L-L voltage) ungrounded or corner grounded system, the phase to ground voltage is meaningless, but the phase to phas voltage will be 460v all around the delta. If you have a 460v system and you're only seeing 230v, there's something wrong.
First of all, a 150 HP 460V 3-phase motor only draws around 170A, so two of them would only draw 340A, not 800. 340A at 460V equals almost 300,000 watts (or 300kw), and the generator would need to be sized a little bigger than this to start such big motors.
Primary : 4 Secondary : 3/0 <<>> To answer this question correctly a voltage must be stated.
That's an 11% overvoltage (460/415), so this may be reaching the design limits of the transformer. If the system is actually run hot (say 105% of 460, or 480v), then I'd say no, unless specifically stated in test reports or design criteria. You should ask the manufacturer to be sure.
60.4
Yes, as long as you use only one phase of the 3 phase system. If R & Y gives 460 volts, use R & Y. This not a good approach though.
The the supply stays within +/- 5% of what the motor is rated for, you can do this.
It will not work at all.
Depending on model and condition anywhere from $1500-850.
My first thought is this is probably a corner grounded delta system, but I'm confused by your voltages. If this was a 460v (L-L voltage) ungrounded or corner grounded system, the phase to ground voltage is meaningless, but the phase to phas voltage will be 460v all around the delta. If you have a 460v system and you're only seeing 230v, there's something wrong.
You can use a voltage converter to step down the 460V 3 phase motor to match the 380V 50Hz supply. Make sure the converter can handle the motor's current requirements. It's also advisable to consult with an electrician to ensure safe and proper installation.
yes can run but motor only delivers 90%rated power because v/f less by 10%
First of all, a 150 HP 460V 3-phase motor only draws around 170A, so two of them would only draw 340A, not 800. 340A at 460V equals almost 300,000 watts (or 300kw), and the generator would need to be sized a little bigger than this to start such big motors.
In the United States, 480 Volts (AC) is a nominal system voltage before it is distributed to the device being powered. Line losses (measured in volts) occur throughout the distribution system due to current passing through wires and devices which have a resistance. Manufacturers of end use devices, such as motors, take this into account and list their devices as 460 volt devices. So, what this means is that you will see transformers and circuit breakers with nameplates at 480 Volts (AC), and motor nameplates at 460 Volts (AC). Older 3-phase motors may actually have nameplates for 440 Volts, but all new motors in this voltage range would be listed as 460 Volt motors.
It would make no sense even if you could find a DC-AC inverter with an input voltage of 720V. The efficiency would be horrible and the bulk of the equipment would be impractical. The voltage your motor expects is 460 VRMS. This translates to a peak voltage of 650V (1300V peak-to-peak). Your battery pack, switched through an H-bridge of IGBT's using a PWM scheme could directly feed the motor. This is the best method available, but the design would not be trivial. Possibly, you could ditch the DC-AC inverter and use just a 460V variable-speed drive with 460V input and 460V output. Bypass the input rectifiers on the drive and use your batteries DC output directly to power it. It's a possibility anyway. You realize, of course, that you are dealing with voltage and power levels that can be fatal, right? Be careful.
Yes, assuming the panel is 460 volt, three phase. You will need to supply a 2-pole breaker of the proper current rating. The breaker installs on any two adjacent phases, such as A-B. Any two phases of 460 volt, three phase power will yield 460v single phase.IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOBSAFELY AND COMPETENTLYREFER THIS WORK TO QUALIFIED PROFESSIONALS.If you do this work yourself, always turn off the powerat the breaker box/fuse panel BEFORE you attempt to do any work AND always use a meter or voltage indicatorto insure the circuit is, in fact, de-energized.