It depends on a lot of factors. Generally speaking, if the insulation is THHN then the rating is 350 amps. If the insulation is THWN then the rating is 310 amps. The ampere rating for wire depends on the temperature of the environment it will be used in, the insulation rating and the number of circuits installed in a conduit. There are also other factors to consider... like voltage drop in long runs.
A motor that is rated at 250 full load amps will need 400 amp time delay fuses or a 500 amp frame breaker with adjustable amperage trips. The wire size for this motor has to be 125% of the motors FLA. 250 x 125% = 312 amps. A 350 MCM copper conductor with an insulation factor of 90 degrees C is rated at 325 amps.
A 400 MCM copper conductor with an insulation temperature factor of 90 degrees C is rated at 380 amps.A 500 MCM copper conductor with an insulation temperature factor of 75 degrees C is rated at 380 amps.These conductors can have either 600 or 1000 volt insulation rating depending on what the system voltage in use is.
A zener diode with a rating of 500 mW will pass 50 mA at 10 V. (Power = voltage times current)Note: The question appears mis stated, in that it states a rating of 500 MW, not 500 mW. To my knowledge, there is no zener with a rating of 500 MW.
A 228 sq mm conductor equates to 450 MCM. A conductor of 450 MCM is not a standard AWG wire size. A standard 400 MCM will carry 380 amps. A standard 500 MCM will carry 430 amps. Difference between 400 and 500 MCM amperage's is 50 amps. Transposing between the two amperage's of 50 amps will be 380 + 25 = 405 or 430 - 25 = 405 amps. This is a very rough calculated answer for the question.
Wire sizing is based on the load that the conductors carry. The breaker is then sized to protect the wire. To get to an amperage the wires are going to have to be paralleled. The calculations are already sized in the electrical code books, CEC and NEC. These are code books used by North America electricians. A 500 MCM conductor with an insulation factor of 90 degrees C is rated at 430 amps. Four 500 MCM conductors paralleled will give you an ampacity of 1720 amps. The breaker will need to have a 500 MCM 4 barrel lug to receive the conductors. The same thing with the load end, it will also need a four barrel 500 MCM lug.
A 350 MCM copper conductor with an insulation rating of 90 degree C is rated at 350 amps.
A 750 MCM copper conductor with an insulation factor of 90 degrees C is rated at 500 amps.
This is a voltage drop question. A 500 MCM copper or 750 MCM aluminium conductor will limit the voltage drop to 3% or less when supplying 300 amps for 500 feet on a 240 volt system. Paralleling these conductors will allow the rating to be increased to 600 amps.
No, a 700 amp fuse would not be suitable for a 500 amp circuit. The fuse amperage rating should be equal to or slightly higher than the circuit's maximum amperage to provide proper protection. In this case, a 500 amp fuse or slightly higher would be the appropriate choice.
A motor that is rated at 250 full load amps will need 400 amp time delay fuses or a 500 amp frame breaker with adjustable amperage trips. The wire size for this motor has to be 125% of the motors FLA. 250 x 125% = 312 amps. A 350 MCM copper conductor with an insulation factor of 90 degrees C is rated at 325 amps.
If you know the voltage being supplied, divide that into 500kVA. For example for 120 Volts the amperage would be 500,000/120 = 4166.66 Amps.
A 400 MCM copper conductor with an insulation temperature factor of 90 degrees C is rated at 380 amps.A 500 MCM copper conductor with an insulation temperature factor of 75 degrees C is rated at 380 amps.These conductors can have either 600 or 1000 volt insulation rating depending on what the system voltage in use is.
For a 400 Amp service with 500 MCM conductors, the minimum size grounding electrode conductor required would be 3/0 AWG copper or 250 kcmil aluminum based on the NEC Table 250.66.
A zener diode with a rating of 500 mW will pass 50 mA at 10 V. (Power = voltage times current)Note: The question appears mis stated, in that it states a rating of 500 MW, not 500 mW. To my knowledge, there is no zener with a rating of 500 MW.
A 228 sq mm conductor equates to 450 MCM. A conductor of 450 MCM is not a standard AWG wire size. A standard 400 MCM will carry 380 amps. A standard 500 MCM will carry 430 amps. Difference between 400 and 500 MCM amperage's is 50 amps. Transposing between the two amperage's of 50 amps will be 380 + 25 = 405 or 430 - 25 = 405 amps. This is a very rough calculated answer for the question.
For an 800 amp service with parallel sets of 500 kcmil copper conductors, the grounding electrode conductor size should be based on the largest conductor in the parallel set. The grounding electrode conductor size should be sized based on Table 250.66 in the NEC, which recommends a minimum size of 3/0 AWG copper for 1/0 AWG or larger service-entrance conductors.
Check the nameplate rating on the door or door frame of your washer, it should tell you the amp rating or the kw rating of the machine. If it only has the KW rating of the machine, simply divide the KW rating by the voltage of the receptacle and it'll give you the current (ampere) rating. Typically, a modern washing machine will draw approximately 7-12 amps. However, anticipate a higher amperage when starting the machine as the machine will draw 1.5X the rated current to start the machine (starting current). Regardless of the amp rating, the NFPA-70 (National Electrical Code) requiresa 20 Amp fuse or circuit breaker; and the circuit for the washing machine must be on its own, dedicated circuit.