What is ground fault in the NEC book?

Updated: 10/17/2022
User Avatar

Wiki User

βˆ™ 14y ago

Best Answer

A ground fault is where there is unexpected current on ground. It represents an imbalance between (hot) current supplied and (neutral, or opposing hot) current returned. That imbalance, by Thevanin's current law, must mean there is current on ground.

Usually, a ground fault represents a malfunction or short in the load. Sometimes, it represents a cross tie or interchange of ground and neutral. In any case, a ground fault must be corrected, because it represents an unsafe condition, and because the NEC requires such correction.

Some times this is a bit tricky to see, since neutral and ground are tied together at the distribution panel and at the service transformer. Since the NEC, however, requires isolation between ground and neutral except at the panel, detecting ground fault is somewhat straightforward, usually measured with a differential current transformer, comparing hot and neutral or opposing hot.

I do not have a copy of the NEC in front of me. This is an intellectual answer, but I believe it to be consistent with the NEC's formal definition of a ground fault. Please, anyone with the formal definition, feel free to refine this answer.

User Avatar

Wiki User

βˆ™ 14y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What is ground fault in the NEC book?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

Is a ground fault protection for equipment required even if the neutral will not be used?

Yes, ground fault protection for equipment is requiredeven if the neutral will not be used.However, the question implies that it might not be required if there is a neutral. That is not true. With two exceptions, ground fault protection is always required in the US, and it is probably required in other countries as well.The exceptions are the use of an electric cooking range, and an electric clothes dryer. In those cases, the US NEC allows the neutral conductor to also be the ground fault conductor, except for the case where the range or dryer is in a mobile home. In the case of the mobile home, the ground fault conductor and the neutral conductor must be maintained separate and distinct all the way back to the distribution panel.In every other case, including where local code overrides the US NEC's exceptions, it must be understood that ground fault protection (protective earth ground) is not the same as neutral, even though the neutral conductor is grounded.


The device used to deenergize circuits automatically when a very small ground-fault flows is the?

Ground Fault Circuit Interrupter (GFCI).


Do you need a ground fault breaker for your hot tub?

Yes, the electrical code requires a ground fault breaker for your hot tub.


In the electrical system of the US what is the difference between the neutral and the PE Ground?

US NEC: The neutral conductor is an insulated grounded conductor used as the current return in a circuit. The color designation for neutral is white. The protective ground (PE, protective - earth) is a non-insultated grounding conductor used to shunt fault current to ground, tripping the protective device. The color designation for PE ground is green. Neutral and PE ground are tied together at the distribution panel. PE ground is also connected to a solid earth ground, such as grounding rods driven into the earth. Downstream of the distribution panel, PE ground is never used to carry operational current. Any current flow on PE Ground, other than parasitic current, is considered a ground fault, which must be corrected. In fact, GFCI (Ground Fault Current Interrupting) breakers will trip when neutral current does not match hot current, an indication of PE ground current flow.


Does voltage on ground mean open ground?

Voltage on ground can mean an open ground. It can also mean (high) current on ground, due to a ground fault such as reversed neutral and ground.

Related questions

Is a ground fault protection for equipment required even if the neutral will not be used?

Yes, ground fault protection for equipment is requiredeven if the neutral will not be used.However, the question implies that it might not be required if there is a neutral. That is not true. With two exceptions, ground fault protection is always required in the US, and it is probably required in other countries as well.The exceptions are the use of an electric cooking range, and an electric clothes dryer. In those cases, the US NEC allows the neutral conductor to also be the ground fault conductor, except for the case where the range or dryer is in a mobile home. In the case of the mobile home, the ground fault conductor and the neutral conductor must be maintained separate and distinct all the way back to the distribution panel.In every other case, including where local code overrides the US NEC's exceptions, it must be understood that ground fault protection (protective earth ground) is not the same as neutral, even though the neutral conductor is grounded.


How do you wire a ground fault switch?

To replace the wire ground fault switch, you need to switch off electric power from the source. After switching it off you can use the screwdriver to open screw and remove the faulty switch and replace it with a good one. <<>> There is no such a device as a ground fault switch. There is a ground fault breaker and a ground fault receptacle.


How can one book reservations for NEC hotels?

You can book reservations for NEC hotels online from the Trip Advisor, Booking and Expedia websites. Once on the website, you can view and write reviews and get contact information for the hotels.


How many pages are in the 2005 NEC Code Book?

The paperback version of the 2005 NEC code book has 792 pages. It is written by the National Fire Protection Agency. It is the standart for electrical and wiring regulations.


What do ground fault relays do?

Ground fault relays sense ground faults in the circuit and trigger a circuit breaker to trip off


Is the size of the ground wire important?

Yes, it has to be sized to the main circuit feeders to be able to carry the fault current of the main feeders if a fault occurs. Sizing of ground wires for service supplies can be found in the electrical code book. In cable wire sets the ground wire is determined by the manufacturer of the cable.


What are the types of faults in ehv transmission lines?

The three types are Line to ground faults line to line fault double line to ground fault three phase line to ground fault


Where can I fine the resistance of standed copper wire?

In any NEC code book


What is the GFCI?

The Ground Fault Circuit Interrupter (GFCI) is an electrical device designed to protect against electric shock by quickly cutting off power to a circuit if it detects a ground fault, such as current leakage. It is commonly used in areas where water and electricity may come into contact, such as bathrooms, kitchens, and outdoor outlets.


What is a difference between ground fault and earth fault?

An earth fault relay and an overcurrent relay are both protective devices used in electrical systems, but they serve different purposes and operate based on different principles. Here are the key differences:Function:Earth Fault Relay: Detects ground (earth) faults, which occur when a live conductor comes into contact with the earth or a grounded component. Its primary function is to sense leakage currents to the ground and trip the circuit breaker to prevent damage or hazards.Overcurrent Relay: Detects overcurrent conditions, which occur when the current exceeds the rated capacity of the circuit. This could be due to overloads or short circuits. Its primary function is to protect the electrical system from excessive current that can cause overheating and damage.Detection Method:Earth Fault Relay: Typically uses a zero-sequence current transformer (CT) or residual connection method to measure the imbalance between phase currents, which indicates a ground fault.Overcurrent Relay: Uses current transformers (CTs) to measure the current in each phase and operates when the current exceeds a predetermined threshold.Sensitivity:Earth Fault Relay: More sensitive to small currents, as earth faults often involve low fault currents compared to phase-to-phase faults.Overcurrent Relay: Designed to detect larger currents that exceed the normal operating range of the circuit.Applications:Earth Fault Relay: Commonly used in systems where protection against ground faults is critical, such as in power distribution networks, industrial installations, and consumer units.Overcurrent Relay: Widely used in protecting transformers, motors, generators, and feeders from overcurrent conditions.Configuration:Earth Fault Relay: Usually configured to operate at a lower current setting due to the nature of ground faults.Overcurrent Relay: Configured based on the normal operating current of the circuit and its protection requirements, usually at a higher current setting than earth fault relays.In summary, while both relays are crucial for system protection, an earth fault relay focuses on detecting and isolating ground faults, whereas an overcurrent relay protects against excessive current conditions that can damage equipment and cause safety hazards.


The device used to de-energize circuits automatically when a very small ground-fault current flow is the?

Ground fault interupter.


The device used to deenergize circuits automatically when a very small ground-fault flows is the?

Ground Fault Circuit Interrupter (GFCI).