Multiply the power of the load [1.732 x UL IL x power factor], expressed in kilowatts, by the operating time, expressed in hours. This is only practical for a constant load.
In exactly the same way as you do so for a single-phase load. It's the product of the power of the load, expressed in kilowatts, and the during of operation, expressed in hours. (And the symbol of kilowatt hours is 'kW.h', not 'kwh')
Single phase power from a L-L voltage of 208 volts is calc'd: P = V(phase to phase) * I (individual phase current) / sqrt(3) Total power from all three legs is the above P * 3. P is in watts; continuous sampling will result in watt hour measurements; 1000 x this is kWh's.
3.7 kwh
In a balanced 3-phase system, if the three loads are star connected, the line current is equal to the load current. If the loads are delta connected, the line current is less than the load current by a factor of 1/sqrt(3).
Power is current times voltage, that is, 5 x 220 = 1100 Watts, or 1.1 kW. That's 1.1 kWh/hour, or 2.2 kWh in 2 hours. Note: The formula power = current x voltage is only valid if current and voltage are in phase. If they are not, power may be somewhat lower. (A "power factor" must be included in the calculations in this case, this power factor may be less than one.)
To convert amps to kilowatt-hours (kWh) for a three-phase system, you need to know the voltage. The formula for three-phase power is: Power (kW) = sqrt(3) x Voltage (V) x Current (A) x Power Factor. Once you have the kW, you can convert to kWh by multiplying by the number of hours the equipment operates.
In exactly the same way as you do so for a single-phase load. It's the product of the power of the load, expressed in kilowatts, and the during of operation, expressed in hours. (And the symbol of kilowatt hours is 'kW.h', not 'kwh')
No, a single phase kWh meter is designed to measure the energy consumption of single phase loads only. To measure the energy consumption of a three phase load, you would need a three phase kWh meter specifically designed for that purpose. Using a single phase meter for a three phase load would not provide accurate energy consumption readings.
To calculate the kWh consumed by a 3-phase motor, you'll need to know both the power factor and operating hours. The formula is: kWh = (√3 x Volts x Amps x Power Factor x Hours) / 1,000. Without the power factor and hours of operation, a precise kWh calculation cannot be provided using just voltage and current.
Single phase power from a L-L voltage of 208 volts is calc'd: P = V(phase to phase) * I (individual phase current) / sqrt(3) Total power from all three legs is the above P * 3. P is in watts; continuous sampling will result in watt hour measurements; 1000 x this is kWh's.
3.7 kwh
To calculate three-phase meter reading in kWh with CT coils, you need to first determine the current ratio provided by the CT coils. Multiply the current readings obtained from the CT coils with the current ratio to get the actual current values. Then, multiply the actual current values with the voltage and power factor to get the power in each phase. Finally, sum the power in each phase and multiply by the time in hours to get the kWh reading.
It depends on the voltage. Please restate the question and provide the voltage. In general, however, simply divide total power by KV to get KA. Remember the KWH is an integral, so you need to back calculate KW. If the month is a 30 day month, then KW is KWH / 30 / 1440. Then, if the load is star, simply divide by three; if the load is delta, divide by three and multiply by 1.732, the square root of 3. Example: 480 three phase running star. 8000 / 30 / 1440 is 185 amperes. 185 divided by 3 is 62 amperes per phase. For delta, that becomes 107 amperes.
To calculate kWh from kW and running hours, you can use the formula: kWh = kW x hours. Simply multiply the power in kilowatts (kW) by the running time in hours to get the energy consumption in kilowatt-hours (kWh). This formula helps you determine the total amount of energy consumed by a device or system over a specific period.
To find kilowatt-hours (kWh) from kilowatts (kW), you need to multiply the power in kilowatts by the time in hours that the power is used. The formula is: kWh kW x hours. This calculation will give you the total energy consumed in kilowatt-hours.
In a balanced 3-phase system, if the three loads are star connected, the line current is equal to the load current. If the loads are delta connected, the line current is less than the load current by a factor of 1/sqrt(3).
To convert watts to kilowatt-hours (kWh) in a three-phase system, you need to know the power factor and the duration of time in hours. The formula is: kWh = (Watts x Power Factor x Hours) / 1000. Multiply the power factor, duration in hours, and watts, then divide by 1000 to convert to kWh.