A shunt-trip coil is a built-in component of a shunt-trip circuit breaker. It is a magnetic coil that can be energized externally to make the breaker trip to shut off the flow of current. For instance, fire sprinklers are sometimes required in the top of elevator shafts in case of a fire in the shaft. If the sprinklers were to spray water on the electric controls in the elevator cab, people could be hurt or killed, either from electrocution or from the elevator malfunctioning. In these cases, a shunt-trip breaker is installed in the circuit feeding the elevator controls, and the fire alarm system sends a trip signal if it detects waterflow from the sprinkler system. This trips the breaker and removes power from the elevator cab. Once tripped, a shunt-trip breaker requires a person to reset it manually.
Yes a shunt trip breaker can be activated manually.
A shunt trip breaker is reset the same way as an ordinary breaker, move the handle to the full off position and then to the full on position. First check the tripping circuit, sometimes a latch relay is used to hold the breaker shunt trip coil in the trip position. If this is the case then reset the latch relay first.
Moulded breakers or shunt trip breakers - selection is defined by the current rating requirement.
A shunt capacitor creates a low resistance path in a circuit so that electricity can pass around to another point. Shunt capacitors create shorts when they receive abnormally high amounts of voltage to correct series circuits.
A shunt-trip coil is a built-in component of a shunt-trip circuit breaker. It is a magnetic coil that can be energized externally to make the breaker trip to shut off the flow of current. For instance, fire sprinklers are sometimes required in the top of elevator shafts in case of a fire in the shaft. If the sprinklers were to spray water on the electric controls in the elevator cab, people could be hurt or killed, either from electrocution or from the elevator malfunctioning. In these cases, a shunt-trip breaker is installed in the circuit feeding the elevator controls, and the fire alarm system sends a trip signal if it detects waterflow from the sprinkler system. This trips the breaker and removes power from the elevator cab. Once tripped, a shunt-trip breaker requires a person to reset it manually.
I can only assume that you are attempting to connect 480VAC coil from a elevator to a fire system in order to shunt the elevator. In order to do this you will need a shunt trip breaker rated for this use.
It works just like a normal circuit breaker with one additional function. A shunt-trip breaker also has a built-in magnetic coil that can be energized externally to trip the breaker. For instance, fire sprinklers are sometimes required in the top of elevator shafts in case of a fire in the shaft. If the sprinklers were to spray water on the electric controls in the elevator cab, people could be hurt or killed, either from electrocution or from the elevator malfunctioning. In these cases, a shunt-trip breaker is installed in the circuit feeding the elevator controls, and the fire alarm system sends a trip signal if it detects waterflow from the sprinkler system. This trips the breaker and removes power from the elevator cab. Once tripped, shunt-trip breakers require a person to manually reset them.
shunt trip coil used to trip the breaker automatically or manually.
To wire a shunt trip breaker for testing, connect one terminal of the shunt trip coil to the breaker's trip terminal, and connect the other terminal to the source voltage. When a signal triggers the shunt trip coil, it will cause the breaker to trip as if there were a fault, allowing for testing without an actual fault condition.
Yes a shunt trip breaker can be activated manually.
The cost of a shunt trip breaker depends on the amperage and number of poles the circuit connected to it needs. The cost of the shunt trip over a conventional breaker is substantially more.
Yes, you can. If your shunt trip is 120 volts, just get 120 volt from your panel and take it to your ansul normally open contacts than to your shunt trip braker. than when your ansul system trips it will trip your shunt braker.
No, when a shunt trip breaker trips, it opens the circuit and disconnects the voltage supply to the protected circuit.
Yes, but you need a power source, for the shunt trip coil voltage, in the circuit.
The way to detect if a shunt trip breaker is malfunctioning is to manually trip the breaker. The shunt is usually wired through a auxiliary relay. Make sure that before you trip the breaker that the load can be shut off without taking a production line etc. off line. Trip the auxiliary relay using a test jumper to activate the relays coil. The breaker's handle will move to mid throw and the load will disconnect from the supply power. If the breaker trips then it is working properly. If the breaker does not trip trouble shoot the circuitry that is used to trip the breaker. Usual problem is an open circuit.
A shunt trip breaker is reset the same way as an ordinary breaker, move the handle to the full off position and then to the full on position. First check the tripping circuit, sometimes a latch relay is used to hold the breaker shunt trip coil in the trip position. If this is the case then reset the latch relay first.