answersLogoWhite

0


Best Answer

Typical limit on equipment is 5 uAmps, but you can actually fail testing on a unit that has greater leakage current inherent to design. 1)Limit (usually on the order of kilomegohms) to design or build for depends on the UL, ANSI, or Military spec that is usually called out by a customer. 2)Measured value with DC Megohmeter to look for depends on size of the part, and resistivity of the insulation materials. Resistance between isolated windings will be defined as (area of interface) divided by (thickness of insulators) x resistivity of insulator. Resistivity is normally a listed mfgr value.

User Avatar

Wiki User

15y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

13y ago

The very best reading is infinity. Engineers like to have a reading of 5 megohm. Most situations work well with 2 megohm. I have seem motors operating in severe conditions as low as .5 megohm.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What is an acceptable megger reading for 500 mcm?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

What is the acceptable insulation resistance megger reading of 160 linear feet of 350 MCM copper underground cable phase to phase phase to neutral and phase to ground?

Engineers that I have worked with state in their specifications that all meggered wires must have a reading of 5 Meg ohms or higher. If the reading is lower that this benchmark start checking splices especially if it is an underground installation. Water usually accumulates in underground conduit systems and when the wires are pulled in there is a certain amount of conductor scraping. This starts the downward spiral from infinity. Check termination points close to the exit point of the conduit. A certain amount of evaporation from the conduit condensates on the terminal points.


How much current does 300 sq mm cable carry?

A 228 sq mm conductor equates to 450 MCM. A conductor of 450 MCM is not a standard AWG wire size. A standard 400 MCM will carry 380 amps. A standard 500 MCM will carry 430 amps. Difference between 400 and 500 MCM amperage's is 50 amps. Transposing between the two amperage's of 50 amps will be 380 + 25 = 405 or 430 - 25 = 405 amps. This is a very rough calculated answer for the question.


How can we calculate cable size for 800A breaker?

Wire sizing is based on the load that the conductors carry. The breaker is then sized to protect the wire. To get to an amperage the wires are going to have to be paralleled. The calculations are already sized in the electrical code books, CEC and NEC. These are code books used by North America electricians. A 500 MCM conductor with an insulation factor of 90 degrees C is rated at 430 amps. Four 500 MCM conductors paralleled will give you an ampacity of 1720 amps. The breaker will need to have a 500 MCM 4 barrel lug to receive the conductors. The same thing with the load end, it will also need a four barrel 500 MCM lug.


What is the amperage rating of 500 MCM copper conductor?

It depends on a lot of factors. Generally speaking, if the insulation is THHN then the rating is 350 amps. If the insulation is THWN then the rating is 310 amps. The ampere rating for wire depends on the temperature of the environment it will be used in, the insulation rating and the number of circuits installed in a conduit. There are also other factors to consider... like voltage drop in long runs.


Convert 350 mcm to AWG?

There is no defined AWG for 350 MCM. The American Wire Gauge stops at 0000 (4/0), and 350 MCM is bigger than this. An approximate conversion would be 6/0, if there were such a thing. Extrapolating out from 4/0, 6/0 is 334.8 MCM, and 7/0 is 422.2 MCM. These wire sizes don't exist of course, and don't exactly match 350 MCM anyway.

Related questions

What is the acceptable insulation resistance megger reading of 160 linear feet of 350 MCM copper underground cable phase to phase phase to neutral and phase to ground?

Engineers that I have worked with state in their specifications that all meggered wires must have a reading of 5 Meg ohms or higher. If the reading is lower that this benchmark start checking splices especially if it is an underground installation. Water usually accumulates in underground conduit systems and when the wires are pulled in there is a certain amount of conductor scraping. This starts the downward spiral from infinity. Check termination points close to the exit point of the conduit. A certain amount of evaporation from the conduit condensates on the terminal points.


For a parallel feed to a 1200 Amp service 3 phase what size is the grounding electrode to main service with 3 600 mcm parallel runs?

500 mcm


What is the amp rating of 500mcm?

The amp rating of a 500 MCM (thousand circular mil) cable can vary depending on the insulation type and installation conditions. Generally, a rough estimate for a 500 MCM cable with THHN insulation in a typical installation would be around 380-400 amps. However, it is recommended to consult the manufacturer's specifications or a qualified electrician to determine the exact ampacity for a specific application.


What size conduit for 3 500 mcm wires?

The required size of a conduit raceway for a 3-5000 mcm wire is 300 kcmil. It maximizes the limits on the wire fill for raceways.


What is the number for mcmd?

m = 1000 c = 100 d = 500 MCMD doesn't make sense MCM = 1900 MD = 1500 CM = 900 so it would be MCM + D = 1900 + 500 = 2400, but that would be written MMCD


What is the weight of 500 mcm thhn wire per foot?

2.2 lbs per ft


What gauge is 500 amp cable?

A 750 MCM copper conductor with an insulation factor of 90 degrees C is rated at 500 amps.


How much current does 300 sq mm cable carry?

A 228 sq mm conductor equates to 450 MCM. A conductor of 450 MCM is not a standard AWG wire size. A standard 400 MCM will carry 380 amps. A standard 500 MCM will carry 430 amps. Difference between 400 and 500 MCM amperage's is 50 amps. Transposing between the two amperage's of 50 amps will be 380 + 25 = 405 or 430 - 25 = 405 amps. This is a very rough calculated answer for the question.


What is full form of MCM?

mcm


What is mcm course?

what is mcm corce


If you have a 400 Amp service using 500 MCM What size grounding electrode conductor is required?

For a 400 Amp service with 500 MCM conductors, the minimum size grounding electrode conductor required would be 3/0 AWG copper or 250 kcmil aluminum based on the NEC Table 250.66.


What size copper wire for a run of 500 feet in parallel for a resident with a load of 600 amps single phase 240 volt?

This is a voltage drop question. A 500 MCM copper or 750 MCM aluminium conductor will limit the voltage drop to 3% or less when supplying 300 amps for 500 feet on a 240 volt system. Paralleling these conductors will allow the rating to be increased to 600 amps.