Best Answer

For a perfectly balanced load, with identical loads connected between each line conductor and the neutral conductor, there should be no neutral current. This is because the vector sum of three identical current, displaced by 120o, is zero.

However, for an unbalanced load, there will always be a neutral current because the vector sum of the currents will not cancell.

User Avatar

Wiki User

13y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Is there a current in star connected transformer in neutral side?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

How you can check load connected of transformer?

Measure the current and voltage on the secondary side.


Do all electrical power sources flow to earth e.g. Secondary winding of an isolating transformer with no earth connection on the neutral line?

There are situations where the secondary of a transformer is not grounded and the neutral is not connected to the neutral of the primary. This can cause a potential shock hazard so the secondary side needs to be protected.


Why instruments are connected on low voltage side of the transformer while performing no load test?

since we need to get desired or rated voltage, so if it is connected in high voltage side of the transformer, voltage supply will be more, and hence the current will be more than the required amount. this is the reason why the instruments re connected at the low voltage of the transformer while performing no load test.


What is the standard output current of a transformer when connected to an ac?

There is no 'standard' output current from a transformer. The secondary (output) current depends on the load, and should not exceed the rated secondary current. To find the rated secondary current, you divide the transformer's rated volt amperes by the rated secondary voltage. The above cited answer need more descriptive ; a) V/Z = I, b) V/Z = I + Magnetizing current of the transformer taken from Primary side of the transformer.


Why load is always connected to secondary of transformer?

b'coz at the secondary side large amount of current flow by recarding of active component or other ckt. which is connected to the secondary side so that ckt. is not damage or burned by flowing large amount .. load is connected at the secondary side .AnswerThe 'primary' winding of a transformer is, by definition, whichever winding is connected to the supply, whereas the 'secondary' winding is whichever winding is connected to the load. This does not mean that a load MUST be connected to a transformer, as it will work 'off load' -that is, with no load connected- without any harm.

Related questions

How you can check load connected of transformer?

Measure the current and voltage on the secondary side.


Which side of a transformer is the load connected to?

It is connected to the secondary side.


In D.C supply the transformer is not connected why?

In a DC power supply a transformer is connected. The only time there would be no transformer used would be if the DC voltage wanted was 120 VDC. The transformer in the power supply is connected to 120 VAC on the primary side and the secondary side of the transformer is connected to either a half wave or a full wave diode bridge. The voltage out of the diode bridge will be the same output voltage potential as the transformer's secondary voltage but it will be a DC (Direct Current) potential.Reading the question in another way, transformers are not connected in a DC circuit. The reason being is that the transformer operates on a collapsing magnetic field. This field induces a voltage into the secondary side of the transformer. Since the DC circuit does not operate on the principle of a collapsing field except when the circuit is opened, the transformer would not operate as a transformer should..


Do all electrical power sources flow to earth e.g. Secondary winding of an isolating transformer with no earth connection on the neutral line?

There are situations where the secondary of a transformer is not grounded and the neutral is not connected to the neutral of the primary. This can cause a potential shock hazard so the secondary side needs to be protected.


How tertiary winding of power transformer acts as stabilizing winding?

in star-star neutral transformer at unbalanced load condition zerosequnce current will be flows in secondary side but this current can not be balanced by primary side because its not having neutral to circulate zerosequence current.due to this unbalance voltage will appeared in primary side but the tertiary delta winding allows circulate the zerosequence current so the primary voltage will get stabilized.


What happens to the current as the voltage is increased by the step up transformer?

Compare a transformer to a balancing act. Both side need to remain equal.The primary side of the transformer is the supply side and the load is connected to the secondary side of the transformer.The load governs the current of the secondary side of the transformer and the voltage of the secondary side must match the voltage that the load required to operate.The ratio of the transformer will determine what the voltage of the secondary side is as compared to the voltage that has to be applied to the primary.The current of a step up transformer will be higher on the primary side that that of the secondary.Apply voltage and current to this concept and you will see that the transformer will remain balanced.The size of the transformer is always calculated from the secondary side of the transformer and the value is written in VA or KVA where V = voltage and A = amperage. Power factor is also taken into consideration when calculating the size of the transformer to be used.


Why instruments are connected on low voltage side of the transformer while performing no load test?

since we need to get desired or rated voltage, so if it is connected in high voltage side of the transformer, voltage supply will be more, and hence the current will be more than the required amount. this is the reason why the instruments re connected at the low voltage of the transformer while performing no load test.


What is the standard output current of a transformer when connected to an ac?

There is no 'standard' output current from a transformer. The secondary (output) current depends on the load, and should not exceed the rated secondary current. To find the rated secondary current, you divide the transformer's rated volt amperes by the rated secondary voltage. The above cited answer need more descriptive ; a) V/Z = I, b) V/Z = I + Magnetizing current of the transformer taken from Primary side of the transformer.


Why there is zero volt across neutral earth of isolation transformer?

Geez, because it is just that; A NEUTRAL EARTH, there should be equal potential on each side, therefore no current flow, and no voltage.


Why load is always connected to secondary of transformer?

b'coz at the secondary side large amount of current flow by recarding of active component or other ckt. which is connected to the secondary side so that ckt. is not damage or burned by flowing large amount .. load is connected at the secondary side .AnswerThe 'primary' winding of a transformer is, by definition, whichever winding is connected to the supply, whereas the 'secondary' winding is whichever winding is connected to the load. This does not mean that a load MUST be connected to a transformer, as it will work 'off load' -that is, with no load connected- without any harm.


How is current controlled in welding transformer?

in welding machine, the transformer used is basically a current transforrmer. so by changing the tap of secondary side of transformer, we can increase or decrease the current in the transformer.


What is the load side of a transformer?

The load side of a transformer feeds the device, such as a light or motor. It is the output of the transformer. The input, or line side, provides the voltage that is to be transformed, either up or down, to supply the load side.AnswerA transformer's primary winding is connected to the supply voltage, and the secondary winding is connected to the load.