If the phase voltage is 230 V, then (providing you are describing a three-phase, four-wire, system), then the line voltage will be 1.732 larger -i.e. 400 V.
The single phase voltage in India is 230v when we check with the phase and the nutral single line
The single phase voltage in India is 230v when we check with the phase and the nutral single line
The first figure indicates the phase to neutral or ground voltage and the second is the phase to phase voltage. i.e. Vph-ph = 1.732Vph-n
If the motor is a three phase the most likely voltage the motor operates on will be 480 volts.
To answer this question a voltage needs to be stated and whether the load is three phase or single phase. Without the voltage the amperage can not be calculated. For single phase, Amps = kva x 1000/voltage, for three phase, Amps = kva x 1000/1.73 x voltage.
The single phase voltage in India is 230v when we check with the phase and the nutral single line
The single phase voltage in India is 230v when we check with the phase and the nutral single line
In India its 415V, 50Hz.
It is 230V single phase and 440V in 3 phase system at 50 Hz.AnswerIf the single-phase voltage is 230 V, then the three-phase voltage must be 400 V, not 440 V. The line voltage is 1.732 times the phase voltage.
The first figure indicates the phase to neutral or ground voltage and the second is the phase to phase voltage. i.e. Vph-ph = 1.732Vph-n
If the motor is a three phase the most likely voltage the motor operates on will be 480 volts.
To answer this question a voltage needs to be stated and whether the load is three phase or single phase. Without the voltage the amperage can not be calculated. For single phase, Amps = kva x 1000/voltage, for three phase, Amps = kva x 1000/1.73 x voltage.
It depends on (1) its voltage rating, and (2) whether it is single phase or three phase. And the symbol for kilovolt ampere is kV.A -not 'kva'.
To answer this question a voltage and HP must be stated.
No. You need a 3-phase supply that matches the voltage and current rating of your appliance.
The phase-to-phase voltage of a 66kV earthed cable would be 66kV. Earthed cables typically have the same voltage rating for phase-to-phase and phase-to-ground connections. The neutral point of the cable is connected to ground for safety and operational reasons.
There is phase to phase voltage in 3 phase system.AnswerYou don't get voltage 'phase-to-phase'; it's 'line-to-line'!