since at no load only excitation current(responsible for core loss ie iron loss) flow on the primary side so core loss current will be 1A and core loss = v1*i1*powerfactor. core loss = 1*11000*0.24= 2640watt.

User Avatar

Wiki User

12y ago

Still curious? Ask our experts.

Chat with our AI personalities

DevinDevin
I've poured enough drinks to know that people don't always want advice—they just want to talk.
Chat with Devin
EzraEzra
Faith is not about having all the answers, but learning to ask the right questions.
Chat with Ezra
SteveSteve
Knowledge is a journey, you know? We'll get there.
Chat with Steve
More answers

a 11000/400v distribution transformer takes no load primary currnt of 1a at a power factor of 0.24 lagging Find (1) core loss current (2) iron loss

User Avatar

Wiki User

15y ago
User Avatar

Add your answer:

Earn +20 pts
Q: How Core Loss is dependent on Frequency?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

How do you minimize core losses?

Hysteresis and eddy current loss constitute core loss. It can be reduced by replacing solid core by laminated core... by adeeb


Does a transformer changes the frequency of incoming supply?

Yes the transformer effects the incoming frequency supply. This frequency is dependent on the core lamination of the transformer the weightier the core lamination the lesser will be the frequency we get and vice verse..


What is iron loss?

Iron losses (Pi) are independent of of load which occur due to pulsation of flux in the core. Iron losses include both Hysteresis loss and eddy current loss and is same at all the loads.


Is core loss same as no load loss in transformer?

Yes, that is almost true, apart from a very small copper loss in the primary winding that carries the small magnetising current. The core loss (iron loss) depends on the applied voltage. This loss is measured by the open-circuit test, carried out at the working voltage.


In transformer if frequency are reduce then what happen?

t's basically a matter of the magnetizing inductive reactance which is inversely proportional to frequency. You want to keep the magnetizing current low to minimize power loss and avoid saturating the core. The higher the frequency, the lower the required inductance for a given inductive reactance and magnetizing current, thus the smaller the required core and/or number of turns on the windings.Magnetizing current is a normal parasitic byproduct of the transformer inductance and the applied voltage level and frequency. The amount of power that can be transferred through a transformer is usually limited by the transformer winding resistances and is unrelated to the magnetizing current. Thus core size goes up at higher power levels due to larger required wire size, not due to any core limitations.