Littlewatts:
If your question is "Why doesn't the neutral carry current to ground, instead of back to the transformer?" then:
It's important to remember current flows in loops. "Ground" is a reference. If you have a single phase transformer, power will flow out of the transformer, through the hot wire to your wall outlet, and back out the neutral wire, then back to the transformer (likely the center tap of the transformer so you have 120 and 240 volts to your house). It is likely the transformer is grounded, so the center tap is at the same voltage as ground, but since there's a perfectly good wire connecting the return wire to the transformer, the current doesn't have to try to go through the ground back to the transformer.
If your question is "Why isn't current flowing in the neutral wire?", then:
In three phase power, with a three phase 4 wire system (the fourth wire is the wye-neutral) there should be little to no current flowing in the neutral. This is because the three phases are balanced - they are of the same magnitude, 120 degrees apart. If you took an instantaneous snapshot of this and referenced to one of the three currents, you would see something like this: Phase 1 = 10Amps, 0 degrees, Phase 2 = 10Amps, -120 degrees, Phase 3 = 10Amps, 120 degrees. If you summed these together, you will see they sum to zero. This summation is what will flow in the neutral. If there is a slight unbalance between the three (say one is 10.1 Amps), you will see some current in the neutral.
If you're referring to your home, where you likely have single phase, and have three prong outlets, the neutral should be carrying the return current from the hot wire. This is not to be confused with the ground plug (the round one), which should not be carrying any current. The purpose of this plug is to provide a low resistance path to ground in the event something bad happens (so the current chooses this wire to flow in instead of you).
There is the chance that you're connected to an ungrounded system. This would likely have three wires instead of four. In this case, there is no neutral. Without knowing exactly what you're measuring it's difficult to provide a clear, short and concise answer.
<><><><><>
Alex156:
Other answer (explains how a circuit works in detail): Because it is not designed to. The neutral line carries the 'return' current; whereas the ground line is reserved as an unobstructed bypass for emergency current drain.
Neutral does not "carry current to ground". Neutral carries current to some return point, which may or may not be grounded. Neutral, however, is always grounded at some point which, conversely, may or may not be the return point.
Confusing? Seemingly reverse defined? Then you better pay attention, because understanding is critical.
Take a light bulb, a switch, a battery, and three pieces of wire, and series connect them. You can turn the lamp on and off by closing and opening the switch.
This is a standalone circuit, and it is not grounded anywhere. It works just fine.
What is the voltage on the battery anode?
Wait! Before you say 1.5VDC you better be asking "with respect to what?"
Well, lets connect battery cathode to ground. Stop and think about this little circuit. You can still turn the bulb off and on by opening and closing the switch.
What did the ground do?
Absolutely nothing - or absolutely something - depending on your point of view...
There is no current on the grounding wire. None. Nada. Zilch. Try it with a micro-ammeter; except for parasitic leakage, there will be nothing.
Now what about that wire going from the cathode to the near terminal of the switch or bulb (depending on how you wired it)? That carries current, don't you say. More on this later.
Back to the "absolutely something" part... That grounding wire provided a connection from some arbitrarily chosen point in the circuit (it could have been the anode, for all I care) to some well defined ground, ground being defined as the common connection between multiple connections that all wind up connected together to the dirt, i.e. ground.
If you measure the voltage on the anode with respect to ground then, lo and behold, you have 1.5VDC. Why? Because you created a circuit with the meter.
Now, go back twelve paragraphs, to my (Alex146) second paragraph... I said "at some point". I'm going to get picky and say "at one and only one point". This point CANNOT be overemphasized, because, with only one point, there can be no current; and with more than one point, there can be no safety
Hence, the neutral does not carry current to ground - it carries current back to the power return point. Conversely, the grounding conductor never carries current except in a fault condition.
Oh - a new word - fault...
Lets modify the circuit and put a 1 ampere fuse between the battery anode and the rest of the circuit. That fuse is effectively a piece of wire because its resistance is very much lower than the bulb, but not as low as the wires. Things still turn on and off. OK?
Now, lets create a fault by connecting a wire between the load side of the switch and ground (across the light bulb). This is a short circuit.
With the switch open, nothing happens. With the switch closed, two things happen. The battery attempt to deliver infinite current, which it cannot, and the extra piece of wire, be a machine frame or whatever, becomes electrified, potentially creating an electrocution/fire hazard, i.e. extra voltage/current where it should not be.
If the original circuit was still ungrounded, the lamp would still light, but the battery cathode would become -1.5VDC with respect to ground. This offsetting of voltage isn't a big deal in single phase power, but can raise three phase power voltage levels with reference to ground to 1.732 times what they should be, which can initiate fault conditions in other phases. Computer like equipment (called protective relays) are used to detect these overvoltage conditions and hopefully warn operators and take care of any potential problems before a full fault develops.
If, on the other hand, the circuit were grounded, then the short circuit would cause the fuse to blow before any wiring could be damaged and, hopefully, before anyone could get electrocuted.
This all sounds trite doesn't it? Well, it turns out that a lot of engineers spend time designing adequate grounding systems, as well as designing the National Electrical Code (US); and I will assure you that they do not do so just because they "want to".
The "hot" wire and the neutral wire both carry current (the same amount, in fact) when a load is connected to complete the circuit. The ground wire never carries current except when a fault-to-ground situation occurs. Yes, neutral and ground wires should both be at ground potential, but NO they should not be connected at the outlet.
Neutral is the common return, and it expected to be a current carrying conductor. Earth (or ground), on the other hand, is a protective conductor that is not expected to carry current. It is there to provide a path for current in the event of fault, and to trip the protective device, i.e. fuse or circuit breaker. Earth is also not usually insulated, so it is not rated to carry current other than long enough to trip the protective device.
A neutral wire provides a return path for the hot lead while an earth or "ground" wire is provided as a safety function only that is not normally intended to carry current except for the purpose of operator protection.
A ground is not expected to carry any current. It's only there in case of a fault condition. If you have a current reading through a ground wire there is a fault that needs to be corrected. Many times a lazy electrician who couldn't find a broken neutral connected a receptacle or light fixture to ground to make it work. This is not a proper use of the grounding system, and it is dangerous and should be corrected if encountered. The grounding conductor should have at least the same ampacity of the largest phase conductor connected to the circuits it protects. That way it is capable of carrying the full current of the largest conductor in case of a fault.
For carrying Short Circuit Test on Power Transformer Do the following: 1] Isolate the Power Transformer from service. 2] Remove HV/LV Jumps and Disconnect Neutral from Earth/Ground. 3] Short LV Phases by Cu/Al plate which could withstand short circuit current and connect these short circuited terminals to Neutral 4] Energise HV side by LV supply (440 3ph Supply) with OLTC tap position on Normal. 5] Measure Current in Neutral, LV line voltages, HV Volatage and HV Line Currents on various OLTC Tap position. Analysis: If Neutral current is near to zero transformer windings are OK If Neutral current is higher or equal to Line current between LV Phase one of the winding is Open.
No. Absolutely not. The ground conductor is not rated to carry constant current flow. It is only rate to carry fault current flow.
The neutral wire is connected to the ground at the service entrance, providing a return path for current. In a closed AC circuit, the neutral wire carries the difference in current between the hot wires, so the net current flow through the neutral wire is minimal. This is why the neutral wire may appear to carry little to no current in a closed AC circuit.
The "hot" wire and the neutral wire both carry current (the same amount, in fact) when a load is connected to complete the circuit. The ground wire never carries current except when a fault-to-ground situation occurs. Yes, neutral and ground wires should both be at ground potential, but NO they should not be connected at the outlet.
US NEC: The neutral conductor is an insulated grounded conductor used as the current return in a circuit. The color designation for neutral is white. The protective ground (PE, protective - earth) is a non-insultated grounding conductor used to shunt fault current to ground, tripping the protective device. The color designation for PE ground is green. Neutral and PE ground are tied together at the distribution panel. PE ground is also connected to a solid earth ground, such as grounding rods driven into the earth. Downstream of the distribution panel, PE ground is never used to carry operational current. Any current flow on PE Ground, other than parasitic current, is considered a ground fault, which must be corrected. In fact, GFCI (Ground Fault Current Interrupting) breakers will trip when neutral current does not match hot current, an indication of PE ground current flow.
The ground wire should carry no current at all, it is there in case of a short circuit to carry the (short circuit) current back to the breaker panel to trip the breaker. The neutral will carry the unbalanced load current between the 240 volt legs. e.g. L1 and N (neutral) 120 volts the load draws 8 amps. L2 and N (same neutral) 120 volts the load draws 12 amps. The difference between the two amperages is what the neutral will carry 12 - 8 = 4 amps.
Earth is neutral, but only at the distribution panel and upstream from it. Downstream of the distribution panel, earth and neutral shall not interchange or cross connect their connections or their roles - earth is protective ground - and neutral the current carrying return conductor.
The names of common appliance wires include live, neutral, and ground wires. Live wires carry electrical current, neutral wires complete the circuit by returning current to the source, and ground wires provide a path for electricity to safely discharge in case of a fault.
To carry the unbalanced load current.
The hot wire carries current to the appliance, while the neutral wire returns the current back to the power source. Both wires are considered "hot" because they can carry electric current, but the hot wire is at a higher voltage compared to the neutral wire. It is important to keep them separate to maintain the circuit's intended flow of electricity and prevent electrical hazards.
In a 220V outlet, the neutral wire is typically not used. Instead, you will have two hot wires and a ground wire. The two hot wires carry the voltage to the appliance or device, while the ground wire provides a path for any stray current to safely dissipate.
* * * DANGER * * * DANGER * * * DANGER * * *Do not, under any circumstances, use earth ground instead of neutral in a circuit. Besides being a violation of the US National Electrical Code, and probably the applicable electrical code for any country that has an existing neutral system in place, it constitutes a hazard because the earth ground conductor is not rated to carry operational current. It is only there to carry momentary fault current so as to trip the protective device (fuse or circuit breaker) in the distribution panel. Also, placing operational current on protective earth ground can raise the voltage on that conductor, creating the potential for an electrocution hazard.
In a three-phase power transmission system, the neutral conductor does not carry current during normal operation when the system is balanced. The neutral conductor is only used to provide a return path for unbalanced currents in the system and does not carry current when the system is operating under balanced conditions.