A current transformer is used in high voltage circuits where it is not possible to measure current directly. A CT is a step up transformer with only one turn in primary. There will be as many cores based on the purposes like metering, protection etc. The secondary of a CT should never be kept open circuited bcoz very high flux will be developed in the secondary and hence it may be damaged.
Leakage reactance is useful for limiting the short circuit current in transformer and generators. therefore normally the reactance of transformer varies for 4.5% for distribution transformer to 12.5% for 400KV class.
Unit or say Rating of transformer is in KVA and not in KW because copper loss of a transformer depends on current and iron loss on voltage. Hence, Total transformer loss depends on volt-ampere ( VA ) and not on phase angle between voltage and current i.e. it is independent of load power factor. That is why Unit or say Rating Of Transformer Is In KVA and not in KW.
If the frequency is kept the same, you will overexcite the transformer, and it will draw excessive current (similar to inrush currents). Insulation tests are performed on transformers above nominal voltage, but they are performed at higher than rated frequency to keep the volts per hertz roughly equal to prevent overexciting the core.
If you are referring to a pole-mounted distribution transformer, it's in order to maintain a safe clearance between its high-voltage connections and ground level.
To prevent the appearance of a dangerously-high secondary voltage across its terminals.
it is keep open so as to supply voltage to the loadAnswerThe secondary winding of a transformer is NOT necessarily kept open, unless you want to disconnect its load.
Secondry of CT should never kept open during functioning
A current transformer is used in high voltage circuits where it is not possible to measure current directly. A CT is a step up transformer with only one turn in primary. There will be as many cores based on the purposes like metering, protection etc. The secondary of a CT should never be kept open circuited bcoz very high flux will be developed in the secondary and hence it may be damaged.
major losses in the transformer in the volt-ampers.AnswerA transformer's iron losses depend on the magnitude of the flux which, in turn, is proportional to voltage, while its copper losses depend on the winding currents. As both iron and copper losses contribute to the maximum operating temperature of the transformer, it follows that a transformer must be rated in terms of voltage and current. In alternating current systems, the product of voltage and current is apparent power, expressed in volt amperes.As a transformer's secondary voltage is kept approximately constant, it is its 'volt ampere' rating that determines its maximum (secondary) load current.Expressing a transformer's rating in watts (i.e. true power) would be completely meaningless because, with a highly-reactive load, it will be supplying practically zero watts while still possibly having to supply its rated current.
Yes the transformer effects the incoming frequency supply. This frequency is dependent on the core lamination of the transformer the weightier the core lamination the lesser will be the frequency we get and vice verse..
kVA is essentially power rating (capacity) of a transformer. Since power is equal P=I*V, so P=kV*A, with I measure in Amps or denoted as A.AnswerA transformer's iron losses depend on the magnitude of the flux which, in turn, is proportional to voltage, while its copper losses depend on the winding currents. As both iron and copper losses contribute to the maximum operating temperature of the transformer, it follows that a transformer must be rated in terms of voltage and current. In alternating current systems, the product of voltage and current is apparent power, expressed in volt amperes.As a transformer's secondary voltage is kept approximately constant, it is its 'volt ampere' rating that determines its maximum (secondary) load current.Expressing a transformer's rating in watts (i.e. true power) would be completely meaningless because, with a highly-reactive load, it will be supplying practically zero watts while still having to supply its rated current.
Leakage reactance is useful for limiting the short circuit current in transformer and generators. therefore normally the reactance of transformer varies for 4.5% for distribution transformer to 12.5% for 400KV class.
A CT attempts to push a specific ratio of primary current through the secondary. If the secondary burden is a very high resistance (as in an open circuit), the voltage developped across the secondary will build up until it reaches the theoretical limit of the primary voltage. Before it gets to this voltage, it will arc across the air gap in the secondary open (often between two terminal blocks). As an old tech once told me, you only open the secondary of a CT once...the arcs can be fairly spectacular.
Unit or say Rating of transformer is in KVA and not in KW because copper loss of a transformer depends on current and iron loss on voltage. Hence, Total transformer loss depends on volt-ampere ( VA ) and not on phase angle between voltage and current i.e. it is independent of load power factor. That is why Unit or say Rating Of Transformer Is In KVA and not in KW.
none
If the frequency is kept the same, you will overexcite the transformer, and it will draw excessive current (similar to inrush currents). Insulation tests are performed on transformers above nominal voltage, but they are performed at higher than rated frequency to keep the volts per hertz roughly equal to prevent overexciting the core.