why need dielectric test for transformer
When you say BDV you might mean the dielectric strength of transformer oil. A new transformer oil should have at lest a dielectric strength of 39 KV. from a British standard.Transformer oils used are normally tested using ASTM D877-82 with the KV strength tester using 1" electrodes spaced 0.1" apart and the test voltage increased at 3,000 volts/min until it breaks down. The average Kv obtained after 8 trials is considered the Oil dielectric strength.Using this test method,dielectric strength at 30 kv and above is considered good. Dielectric strength between 23 to 29Kvis considered usable, but requires filtering. Below 23 kv, the transformer oil should be replaced.Another method ASTM D18747-82 uses the small radius electrodes but spaced only .o4 inches. The test voltage is 500volts/min and increased until breakdown. The dielectric strength is still the average Kv obtained in 8 trials. The dielectric strength of 28-29Kv is considered good. Below 28 kv, the transformer oil is usable but requires filtering. The latter method is considered a better test method
Kilovolt or 1000 volts. 1KV is 1000 volts, 2KV is 2000 volts. Kilo stands for 1000.
The Dielectric Discharge (DD), sometimes called re-absorption current, test is performed during the discharge cycle after the test. There are three components of current (charging, polarization and leakage currents) present during a standard insulation test, which make it difficult to determine the dielectric discharge. Rather than measuring the polarization current during an insulation test, the DD test looks at the de-polarization and capacitive discharge currents at the conclusion of the insulation test. The device under test (DUT) must be charged for an adequate amount of time to be stabilized therefore, the only remaining current component is leakage current. The DUT is then discharged at the completion of the insulation test and the current flow is measured during a standardized time of one minute. This current is dependent on the overall capacitance and the ending test voltage. Dielectric discharge is calculated as: Dielectric Discharge = I (after 60 seconds) / Volts x Capacitance The DD test can identify excess discharge currents that happen when a layer of multi-layer insulation is damaged or contaminated. This condition will be missed by both the spot test and the Polarization Index test. Discharge current will be higher, for a known voltage and capacitance, if an internal layer is damaged. The time constant of this individual layer will differ from the other layers, causing a higher current than for insulation that is good. Homogenous insulation will have a DD value of 0 while good multi-layer insulation could have a value as high as 2. Source: http://www.aemc.com/
This is a test usually used when performing a insulation resistance on a transformer. This test (result) can be optained by deviding the 30 sec reading into the 60 sec reading. This test recognizes the fact that "good" insulation will show a gradually increasing IR after the test voltage is applied.
dielectric strength is tested by transformer dielectric strength oil testing machine. at first, oil which is to be tested is pour near the two electrode. both the electrode should be dipped in oil . then adjust the distance between the electrode .now start the machine.when a sound came from machine then note down the dielectric strength of the oil.
why need dielectric test for transformer
When you say BDV you might mean the dielectric strength of transformer oil. A new transformer oil should have at lest a dielectric strength of 39 KV. from a British standard.Transformer oils used are normally tested using ASTM D877-82 with the KV strength tester using 1" electrodes spaced 0.1" apart and the test voltage increased at 3,000 volts/min until it breaks down. The average Kv obtained after 8 trials is considered the Oil dielectric strength.Using this test method,dielectric strength at 30 kv and above is considered good. Dielectric strength between 23 to 29Kvis considered usable, but requires filtering. Below 23 kv, the transformer oil should be replaced.Another method ASTM D18747-82 uses the small radius electrodes but spaced only .o4 inches. The test voltage is 500volts/min and increased until breakdown. The dielectric strength is still the average Kv obtained in 8 trials. The dielectric strength of 28-29Kv is considered good. Below 28 kv, the transformer oil is usable but requires filtering. The latter method is considered a better test method
The alternative name for the germ tube test is "Reynold's test."
Another name for a test could be an examination or an assessment
Annually
pentathlon
the answer to your question is Pentathlon that is the name of the 5 test of strength and skill.
An Oil Dielectric Strength Tester is the standard for qualifying Transformer Oil. Thermal Stability would involve heating and then testing. I do not know of a product which controls heat and applies the HV test.
if you have the wii you can find your self doing balance test and or strength test.
Hemoccult Test is the brand name. The generic name of the test is guaiac test. Seroccult is another common brand name.
another name for test tube is culture tube or sample tube