How do you calculate 3ph AC motor power?
250 kVA generators come in different voltage settings and this information is needed before a wire size can be given
First and foremost is the information the manufacturer puts on the nameplate of the motor. Second, the generic amperage can be found on motor charts that are on the Internet. Third you can use a formula to find the approximate amperage. HP = Amps x Volts x 1.73 x pf/746. Transposed for Amperage, Amps = HP x 746/Volts x 1.73 x pf. Use pf = .9 Amps = 10 x 746/ 208 x 1.73 x .9 = 7460/323.85 = 23.03 amps. See how much easier it is to read the nameplate.
Most 3ph Motors are rated for both voltages. High Voltage Wiring (440-480) Connections goes as follows L1=>T1,12 L2=>T2,10 L3=>T3,11 4=>7 5=>8 6=>9. Low Voltage (220-240) goes as follows L1=>T1,6,7,12 L2=>T2,4,8,10 L3=>T3,5,9,11. "L" Denotes Line Side Voltage (Power Coming to the Motor) "T" Denotes Terminal Motor Leads. You may not have #10, 11,or 12 leads as most motors since the 1980's have been internally wired inside the windings to T1, T2, and T3 or 1, 2, and 3 which are the same wires. Usually the Junction box on the side of the motor has this already listed under it's cover. If it shows a Low and a High Configuration, you have a Dual Voltage Motor.
400 amps
In most applications 200v is easier to get for a supply voltage than 380v.
How do you calculate 3ph AC motor power?
Yes.
It will not work at all.
The 3PH motor has no internal contacts for a centrifugal switch and are therefore more durable when switched on and off frequently,
Ph such a three phase is 3Ph for example
Hi there are a few options. The one I chose was to use a VFD (variable frequency drive). First though if you want to run off true lower voltage you will need to check that the motors can be reconfigured to run as delta instead of star. If you look at the motor plate this should give you some idea. If you are lucky the motor terminals will have links that let you move them to reconfigure. If not you will have to research further on the net. If you use a vfd instead of a rotary or static inverter then you will have to connect the output of this directly to the motor ie with no switches in between. All the control like forward, reverse etc are them controlled as low voltage inputs to the inverter. With a rotary or static inverter it is possible to feed the output of these inverters to the supply of the existing wiring but motor voltages and contractors may not work on the reduced supply.
power , P=1.732*V*I*power factor so, the formula for calculate the load current for a 3 phase motor is,I=P/(1.732*V*power factor)
2-3ph
Yes, as long as you use only one phase of the 3 phase system. If R & Y gives 460 volts, use R & Y. This not a good approach though.
In induction motors no seprate source is required to start the motor,and motor itself induces emf as the word induction clearly reflects it starting principle while in case of synchronous motors ,motor is synchronised with an external source of emf.