Power meters are used to measure power used or produced by a customer or generator. A negative power meter reading at a costumer site would mean the costumer is generating electricity that is being pushed back out on the grid, or (more likely) the customer figured out how to reverse the meter! On older meters, reversing would cause the meter to count down so you could hide how much electricity you were using. Newer customer meters do not have this flaw - they add a magnitude of use (ignore the sign, or direction of power flow).
At a generating site, it would mean power is being sucked into the generator, instead of created by the generator.
AnswerI assume that you are referring to a wattmeter, and not an energy meter?
If this is the case, then a reversed reading simply indicates that either its voltage coil or its current coil has been connected the wrong way around. It can be rectified by reversing the connection to either coil (not both!).
When connecting a wattmeter, it's essential to observe the instrument terminal's 'polarity marks' when connecting the voltage and current coils to the circuit. This is because the currents passing through each of these coils must act in the same direction relative to each other or the instrument will read 'down scale' (i.e. backwards!).
Chat with our AI personalities
Yes. This is usually an indication that either its current coil or its voltage coil has been wired incorrectly.
A watt meter will measure active power, not reactive power.
A wattmeter (not 'watt-meter') will always measure the true power of a load, regardles of whether that load is purely resistive or not. This is because a wattmeter effectively measures the in-phase component of the load current.
The Ammeter XD
K=(voltmeter range*ammeter range*power factor)/wattmeter range