One and half breaker system is an improvement on the double breaker system to effect saving in the number of circuit breakers. For every 2 circuits, 1 spare breaker is provided: Two feeders are fed from two buses via their associated circuit breakers and these two feeders are coupled by a third circuit breaker which is called tie breaker. During failure of any of the two feeder breakers, the power is fed via the breaker of the second feeder and main breaker (tie breaker).

User Avatar

Wiki User

10y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What is one and half breaker system in electrical lines?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

Can I wire nut two black wires together and hook 1 to a breaker?

Not according to the electrical code. It requires each separate circuit to be fed individually from its own breaker. If allowed it would reduce the total capacity of each circuit from one amp per outlet to a half amp per outlet if the circuit was fully loaded.The work around in situations like this is to use a tandem breaker which gives you the capacity of two complete circuits and only using one breaker slot in the distribution panel board.


What country has half of the world's geothermal electrical generating capacity?

united states


Is main breaker only powering one half of hot bus because when dryer is on some light on circuits on dead bus work?

Yes, it would appear that one side of the main is open at the fuse, breaker, drop conductors, or transformer.


Why does half of my house have electricity and the other half doesn't with no circuit breakers poped?

as an electrician i would first check the main breaker with a rated voltage tester for voltage i would first ckeck the meter side by placing one tester lead on one of incoming phases or wire and place second lead on the other phase or other wire. i should read 240, or 230, or 220 volts depending on where the taps are in the transformer. if not call the power company. if it does read any of them voltages i would then check the load side of the main breaker by putting my leads on one breaker and the one right below it generally every other breaker is a different phase again i should read 240 volts or close. if not the main breaker may be bad. if you know what breaker or circuit its on you could test it by placing one lead on the screw where the wire is and the other on the neutral or ground bar here you should read 120 volts or close if not breaker is bad. it maybe as easy as tightening the screw or screws so shut the breaker off first and then tighten.


Can you install a main electrical panel in a half bath?

No! Panels are strictly forbidden in bathrooms of any kind. In the NEC, a half bath is a bathroom just as much as a full bath.

Related questions

Why does Half of the electrical box works other half doesn't?

One side of main breaker is broke. One line to the house is open.


What is breaker and a half?

Breaker and a half is a term used in electrical engineering to describe a circuit protection device that has a current rating between one and two times the full load current of the circuit it is protecting. This allows for a margin of safety to accommodate small overcurrents without tripping the breaker.


Will one and a half lines of cocaine be out of system in 3 days?

HECK NO it will take about a month or month and a half for it to come out of your system.


What is one half breaker scheme used for 400220kv substation?

a method of interconnecting several circuits and breakers in a switchyard so that three circuit breakers can provide dual switching to each of two circuits by having the circuits share one of the breakers, thus a breaker and one-half per circuit; this scheme provides reliability and operating flexibility, and is generally used at 500 kV when more than five lines terminate in a substation.


What is the take up on a half-inch breaker?

do you mean bender? If so, 5"


How long of a lunch break did a coal breaker get?

half an hour till Christmas


Can you use two 15 amp single pole breakers in place of a double pole 30 amp breaker?

No, you cannot use two separate 15 amp single pole breakers in place of a double pole 30 amp breaker. A double pole breaker is designed to simultaneously disconnect both circuit conductors, whereas using two single pole breakers would not provide the necessary protection for the circuit. It is important to use the correct size and type of breaker as specified by the electrical code for safety and functionality.


Can I wire nut two black wires together and hook 1 to a breaker?

Not according to the electrical code. It requires each separate circuit to be fed individually from its own breaker. If allowed it would reduce the total capacity of each circuit from one amp per outlet to a half amp per outlet if the circuit was fully loaded.The work around in situations like this is to use a tandem breaker which gives you the capacity of two complete circuits and only using one breaker slot in the distribution panel board.


Why are all the longitude lines labeled e?

E stands for east. Half of the longitude lines are east, the other half are w for west.


How many lines can you get out of half a gram of coke?

It depends on how finely the cocaine is chopped, but on average, a half gram of cocaine can be divided into about 5-10 lines. However, the potency and purity of the cocaine can also affect the number of lines that can be derived from a half gram.


Half of 436 is 217.5--why only 216 votes needed?

The Vice President casts the tie breaker.


How are your movement controlled by the nervous system?

by sending weak electrical pulses through our system. that is also one of the reasons our spine is important, because the electrical pulses are sent through it and it they stop thats when we stop being able to fully use the lower half of our body