It is the rated maximum current that can be taken from the transformer. This is equal to the VA rating divided by the output voltage. So a 6 kVA 240 v transformer would have a maximum current rating of 6000/240 or 25 amps.
transformer action doesn't depend on power factor that is why we indicate its rating in KVA
It depends on (1) its voltage rating, and (2) whether it is single phase or three phase. And the symbol for kilovolt ampere is kV.A -not 'kva'.
Wire sizing of a feed conductor is based on the amperage that a device draws. To calculate amperage from KVA a voltage of the supply has to be stated. Without this voltage and whether the transformer is single or three phase an answer can not be given.
ka of mccb=transformer(KVA)x100/1.732xsecondary voltagex%impedence of transformer
Depends on the kva rating of the devices to be tested using a transformer.
It is the rated maximum current that can be taken from the transformer. This is equal to the VA rating divided by the output voltage. So a 6 kVA 240 v transformer would have a maximum current rating of 6000/240 or 25 amps.
For a single-phase transformer, divide the ratedapparent power (expressed in volt amperes) by the voltage rating (expressed in volts) of the primary winding; this will give you the rated primary current (expressed in amperes) of the primary winding.
yah! definately affects, the kva of transformer is suitable for the certain load according to the rating.
kva*cos(phase angle)
transformer action doesn't depend on power factor that is why we indicate its rating in KVA
The rating of the machine (kva or kw) depends upon the power factor, since the load power factor to which the transformer is supplying power is not known, it may be capacitive, inductive, or resistive that is why its rating is in kva not in kw.
VA or KVA or MVA
You can tap off approximately 833 200 amp panels from a 250 kVA transformer. This calculation is based on dividing the kVA rating of the transformer by the current rating of the panel.
KW is multiplication of KVA and power factor. Power factor is load dependent and varies as per the type of load. Hence the rating or capacity is mentioned in KVA not in KW
It depends on (1) its voltage rating, and (2) whether it is single phase or three phase. And the symbol for kilovolt ampere is kV.A -not 'kva'.
Wire sizing of a feed conductor is based on the amperage that a device draws. To calculate amperage from KVA a voltage of the supply has to be stated. Without this voltage and whether the transformer is single or three phase an answer can not be given.