answersLogoWhite

0


Best Answer

three phase load is said to be balanced when the impedance and power factor of each load is equal.in this condition phasor sum of currents and phase voltages add up to zero.

User Avatar

Wiki User

βˆ™ 13y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What is difference between balanced and unbalanced load?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

How much will neutral current be in a 3phase 4-wire y system with a balanced load?

Balanced load means no unbalanced currents, so the neutral current should be near zero.


Is the line is necessary for the balanced star- connected load?

I think you probably mean is a neutral conductor necessary for a balanced star-connected load? If this is what you mean, then the answer is no, it isn't, as the phasor-sum of the phase currents will equal zero. Often, though, it is difficult to achieve a balanced load, so a neutral is then necessary, as it is needed to provide a return path for the unbalanced current -without this neutral, the phase voltages would change and become unbalanced.


What is the effect of an unbalanced load of generators?

An unbalanced load prevents the generator delivering its maximum power. That is because each phase has an equal upper current limit that it can deliver, and in an unbalanced system, if one phase is delivering the rated current it follows that the others are not.


What is three-phase unbalanced load?

A balanced three phase load is where the current flowing in all three phases of the load are reasonably close to each other.Another answerWhen the voltage and measured current draw do not deviate by more than 2 percent under load.AnswerA balanced three-phase load is one in which each of the three loads is identical in all respects (magnitude and phase). Further to the first answer, the three line currents must not all be 'reasonably close', they must be identical -i.e. the same value and phase relationship.


What is difference between cold load and hot load?

hot load occurs when the power is high and the cold load occurs when yhe power is low

Related questions

What is the difference between Kilowatt Meter with balanced load and with unbalanced load?

'Balanced loads' apply to three-phase a.c. loads. A three-phase kilowatt hour meter will measure both balanced and unbalanced loads, when correctly connected.


How do you balance the unbalanced load in 3 phase?

If the load is connected in wye (star) and it has a neutral, then the vectorial-difference of the phase currents will flow in the neutral and there will be no problem. On the other hand, if there is no neutral, then an unbalanced load would cause unbalanced phase voltages.


Is there any difference in values between the two wattmeter method and three wattmeter method if you apply these two methods in same load?

Blondel's Theorem states that you can have one less wattmeter than there are conductors supplying a balanced or unbalanced load. In either case, the sum of the wattmeter readings will give you the total power of the load.


How much will neutral current be in a 3phase 4-wire y system with a balanced load?

Balanced load means no unbalanced currents, so the neutral current should be near zero.


What is mean by balanced and unbalanced load?

There is a lot of confusion amongst consumers that an Unbalanced LoadStabilizer is generally superior to a Balanced Load Stabilizer. To clarifythis myth certain fundamental principles connected with Transformersare given below:1. Definition of Balanced and Unbalanced loads:a. A Three phase Loads on a 3 phase supply system is a Balancedload because it draws equal current from each phase. Three phaseMotors, Converters; Rectifiers using 3 phase input supply arecommon examples of Balanced loads.b. A single phase / 2 phase loads on a three phase system is calledUnbalanced load. Normally Unbalanced loads have to use aneutral wire in the system. The 2 phase loads may not require aneutral.


Is the line is necessary for the balanced star- connected load?

I think you probably mean is a neutral conductor necessary for a balanced star-connected load? If this is what you mean, then the answer is no, it isn't, as the phasor-sum of the phase currents will equal zero. Often, though, it is difficult to achieve a balanced load, so a neutral is then necessary, as it is needed to provide a return path for the unbalanced current -without this neutral, the phase voltages would change and become unbalanced.


When was Unbalanced Load created?

Unbalanced Load was created on 2009-08-04.


What happens if neutral of three phase four wire system is break?

For a balanced three-phase load, the neutral current is zero, so the loss of the neutral would have no effect.However, for an unbalanced load, the 'difference' between the line currents results in a neutral current.So, for an unbalanced load, if no neutral current can flow, then the load's neutral point will no longer remain symmetrical, and the line voltages will become unbalanced. If the unbalance is severe, then individual loads may be subject to over-voltages or under-voltages.


What significance has a power factor in an unbalanced system?

A three-phase 'unbalanced' system refers to the load, as the supply voltages are unaffected by load. So the phase-angle and, therefore, the power factor of each phase will be different -i.e. there will be three different power factors.


How do you find neutral current in star connected circuit?

if it is balanced then neutral current is zero (!,e iR=iY=iB).AnswerFor both a balanced and an unbalanced load, the neutral current will be the phasor sum of the line currents.


Difference between load shedding and blackout?

no difference


What is the difference between a bed load and a dissolve load?

nada