Answer for USA, Canada and countries running a 60 Hz supply service.
The first thing to do at the distribution panel is to turn off the breaker feeding the receptacle's circuit.
To the new two gang light switch box, two wires will go from the wall receptacle, connected black to black and white to white and ground to ground, to the new two gang light switch box and then two more sets of cable wires will leave the new light switch box and proceed up to the new individual light fixture boxes.
In the two gang switch box, first connect the incoming and outgoing ground wires to the ground screw in the new switch box.
Be sure to connect the ground wire around the grounding screw in the light fixture box.
Next the white wires will be spliced together with a wire nut and pushed to the back of the box and then the incoming "hot" wire will be connected across the top of the two new switches.
Pre position the switches in the off position, which is the handle down, before attaching the wires. The "hot" incoming wire connects to two pigtail wires coming from the top screw of the two switches. These three wires will be spliced together with a wire nut and pushed to the back of the new switch box.
The two black outgoing wires that feed the new light fixture boxes are connected to the bottom screws of the individual switches.
When either switch is turned to the on position, voltage will be applied to the appropriate fixture junction box.
As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed.
Before you do any work yourself,
on electrical circuits, equipment or appliances
always use a test meter to ensure the circuit is, in fact, de-energized.
IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOB
SAFELY AND COMPETENTLY
REFER THIS WORK TO QUALIFIED PROFESSIONALS.
You need a three way switch to control lights from two locations. The name is misleading. Three way switch refers to the connection points on the switch. You can use a three way switch as a single switch as long as you place hot wire on the brass screw and the use any of the other screws for the return hot.
Yes, If you only hook up two wire it will work as a single pole
If you have good access to the wiring this is relatively easy to do. Each of the 10 lights is connected to another in parallel in a "daisy chain" fashion. Light 1 is connected to the switch, light 2 is connected to light 1, light 3 is connected to light 2 and so forth. Let's say it is light 5 that you wish to switch separately. You can first install the new switch by either adding a new box or modifying old switch box. There are two gang switches that will fit the form factor of a single switch. TURN OFF THE POWER TO SWITCH BOX. Using the same supply input at original switch, add a new black wire to the wire nut for input to original switch and connect this to the input of new switch. Then run a new wire to light 5 and connect black wire to the output of new switch. Connect all the white wires together in switch box and separately connect all bare wires together in switch box. Now at light 5 undo the black and white wire coming from the fixture, and reconnect the wire nuts so that there is a direct connection between light 4 and light 6. Do the same for the ground if present (bare wire). You now have the fixture wires hanging free. Now connect the black wire from new switch to the fixture black wire and white to white and you are done.
On these types of installations an electrician would use a three wire cable set from the switch box to the fixture's junction box. At the fixture's junction box both the fan neutral and the light neutral would be wire nutted together with the incoming neutral from the switch boxes. From the three wire, the white wire would go to the fan and light's neutral wires. The Black would come from the bottom of one of the switches and go to the fan's motor lead. The red wire would come from the bottom of the other switch and go to the light fixture's lead. It can be done with two runs of two wire to the fixture. You will need a two gang switch box for this project to hold the two separate switches. You could use a single gang light switch box if you can still find where duplex switches being sold. A duplex switch is one that has the configuration of a duplex receptacle with the switches being one on top of the other. The cover plate is the same one used for duplex receptacles. To answer this question fully more information is needed. See discuss in the left margin.
There will always be voltage to the ground wire, this is normal. The reason being is that the ground wire is bonded to the neutral terminal block back at the distribution panel. If you have a voltage reading to ground at the outside fixture with the switch in the on position then you have an open return neutral wire. This wire should be traced back from the light to the distribution panel. Check ever junction box that the circuit goes through and look for a loose or open white neutral wire. Closing the circuit where you find this fault will correct the problem.
To wire multiple lights to one switch, you can connect the lights in parallel by running a cable from the switch to each light fixture. Make sure to connect the hot wire from the switch to the hot wire of each light, and the neutral wire from the switch to the neutral wire of each light. This will allow you to control all the lights with a single switch.
To wire multiple lights to one switch in a single circuit, you can connect the lights in parallel by running a separate wire from the switch to each light. This allows the switch to control all the lights at once. Make sure to follow proper wiring guidelines and consult an electrician if needed.
To wire two lights to one switch in a single circuit, you can connect the lights in parallel by running a wire from the switch to each light fixture. This way, both lights will be controlled by the same switch. Make sure to follow proper wiring guidelines and consult an electrician if needed.
To wire a double switch with a single dimmer for LED lights, you will need to connect the hot wire from the power source to the common terminal of the double switch. Then, connect the hot wire from the LED lights to one of the switch terminals. Finally, connect the dimmer switch to the other switch terminal. Make sure to follow the manufacturer's instructions and consult a professional if needed.
To have each switch operate a single light, a 3-way switch must be installed for each light. Each switch needs to be wired to its respective light, with one wire running between the switch and light fixture. This way, each switch will control the light it's connected to independently of the others.
To wire 2 lights to 1 switch when the power source is at one of the lights, you will need to connect the power source to the first light, then run a wire from the first light to the second light, and finally connect both lights to the switch. This setup will allow you to control both lights with a single switch.
To wire 2 lights with 2 switches in a single circuit, you will need to connect the power source to the first switch, then run a wire from that switch to the first light. From the first light, run another wire to the second light. Finally, connect a wire from the second light to the second switch. This setup allows you to control each light independently with its respective switch.
To wire a bathroom fan and light to operate on the same switch, you will need to connect the hot wires from both the fan and light to the hot wire coming from the switch. Then, connect the neutral wires from both the fan and light to the neutral wire coming from the switch. Finally, connect the ground wires from both the fan and light to the ground wire coming from the switch. This will allow you to control both the fan and light with a single switch.
run a wire from battery positive to an inline fuse, then to a switch that you have to install in your dash. from the switch to the lights, then to ground. turn on switch, lights should work.
To properly wire a 2 gang switch for controlling multiple lights in a single circuit, you will need to connect the hot wire from the power source to the common terminal of each switch. Then, connect the hot wire from each light to the corresponding switch's load terminal. Finally, connect all the neutral wires together and all the ground wires together. Make sure to follow proper safety precautions and consult a professional if needed.
To wire two lights to one switch, you will need to connect the power source to the switch, then run a wire from the switch to the first light, and another wire from the first light to the second light. This creates a series circuit where both lights are controlled by the same switch. Make sure to follow proper safety precautions and consult a professional if needed.
To properly wire a dual light switch for controlling two separate lights in a single circuit, you will need to connect the hot wire from the power source to the common terminal of the switch. Then, connect the hot wires from each light fixture to the individual terminals on the switch. Finally, connect the neutral wires from the lights and the power source together. Make sure to follow all safety precautions and turn off the power before starting the wiring process.