Watts = Volts times Amps. Therefore, if the voltage was 220 volts, the motor would draw 500 amps. If the voltage was 4,000 volts, the motor would draw 27.5 amps. The voltages for large powerful motors tend to be relatively high, for example in the 380 Volts to 11,500 Volts range.
Depends on the voltage. If you are running off 120 VAC, a 0.5 horsepower motor would draw 3.1 A.
The electrical code states that a 30 HP induction motor at 460 volts three phase will draw 40 amps. <<>> I = 33.34 AMPS IF EFF.= 95% AND P.F.= 85%
The current draw is about 27 amps. A motor feeder has to be 125% of the motors full load amperage. 27 x 125% = 33 amps. A #8 copper conductor with an insulation factor of 90 degrees C is rated at 40 amps.
T430.247 of the NEC shows that a 1 hp motor operating at full load on 115v will draw 16 amps, called Full Load Current (FLC). Conductors supplying this motor are required to be 125% of FLC which is 20 amps. Motor circuits are complicated things and do not follow the rules of other circuits. This motor, while drawing a maximum of 16 amps at full load and supplied with #12 AWG copper conductors can be protected by a breaker of 40 amps.
A single phase 10 HP motor will draw aproximately 50 amps. A three phase 10 HP motor will draw aproximately 28 amps.
Depends on how big the motor is. A stronger motor will draw more amps then a weaker or less efficient motor. For example a wiper motor draws far less then a starter motor.
Excessive resistance (drag), will cause motor to draw more amps (current flow) to operate.
To answer this question the voltage of the motor must be stated.
Watts = Volts times Amps. Therefore, if the voltage was 220 volts, the motor would draw 500 amps. If the voltage was 4,000 volts, the motor would draw 27.5 amps. The voltages for large powerful motors tend to be relatively high, for example in the 380 Volts to 11,500 Volts range.
To calculate the amps drawn by an 18kW motor, you can use the formula: Amps = Power (Watts) / Voltage (Volts). Assuming a standard voltage of 120V, the motor would draw approximately 150Amps. Note that actual amps will depend on the specific voltage of the motor.
For a 1hp 3-phase motor, the current draw will depend on the voltage supply. Typically, at 230V, a 1hp 3-phase motor will draw around 3.6 amps. However, this value may vary based on the motor efficiency and power factor.
It depends on the voltage-- I think at 110v it's 4 amps per hp
Depends on the voltage. If you are running off 120 VAC, a 0.5 horsepower motor would draw 3.1 A.
A typical starter motor draws around 50 to 150 amps while cranking an engine. If the current draw is significantly higher or lower, it may indicate a problem with the starter motor or the electrical system.
read the name plate on the motor
For a 2.5hp 240v continuous motor, the current draw would be around 10 amps. This can vary slightly depending on the motor's efficiency and other factors, but 10 amps is a good estimate to use for this motor.