Dont mess with Transformers if u dont know how to read a wiring diagram It is easy if u know your relation to each of the phases and neutral and ground
Hi first of all Vector group used to determine the PHASE shift of the TRANSFORMER as well as the PRIMARY and SECONDARY connection information. Let taken an example:- YNyn0d1 It means CAPITAL LETTERS indicates the primary side of winding detail's small letters for secondary side detail's DELTA CONNECTION Symbol D OR d is used and connection WYE used Y OR y for PRIMARY and SECONDARY. If WYE connection is their neutral always come so we used suffix N OR n. Now check PHASE angle Difference (PHASE ANGLE) see the last NUMERIC VALUE give correct information. Suppose we connect/compare two TRANSFORMER we first see its VECTOR GROUP if they matched then we do move to any connection. If any quarries fill-free to ask ajay.sahu099@gmail.com
The star connection has three phase terminal leads and one neutral lead. In case of delta connection it has got three phase terminal leads. the star connection is generally represented by Mercedes symbol with neutral line drawn from the mid point. The delta is represented like a triangle symbol with noneutral line shown.
Whether a transformer is 'step up' or 'step down' has nothing to do with the way its windings are connected, so it could be wye-delta or delta-wye.
A star-delta motor should be supplied star-delta.Wye is simply another name for star. Star-delta motors use a star or wye configuration to start, and a delta configuration to run. This reduces the voltage on the windings during the high current starting time.
first you need to touch yourself
An open delta connection is a delta connection with one phase removed, but still supplied with three line conductors. An open wye is a wye connection with one phase removed, supplying a three line conductors and a neutral conductor. An open-delta/open-wye is a method of providing a reduced-load three-phase supply using just two single-phase transformers, rather than the preferred method of using three single-phase transformers.
Motor run delta connection because in delta connection it is less ampere needed and it sometimes it change the wye connection because of the available suply
To terminate a 3 wire wye motor to a 3 phase delta connection you need a 3 phase transformer to convert from delta to wye. Do not lift the common neutral connections inside the motor and rewire for delta, because the voltages will be wrong.
The phase shift in three-phase transformer from winding of Transformer and determine by vectorgroup of transformer such as YNd1 High voltage connect to wye Low Voltage connect to delta so L.V. lag H.V 30 degree.Answer'Phase shift' or, more accurately, 'angular displacement', is the angle between the secondary line voltages and primary line voltages of a three-phase transformer.
For the same load, delta provides higher current than wye, or star.Wye voltage is 1 / 1.732, or 0.577 that of delta. (1.732 is the square root of 3.) This gives a power of 0.333 for wye, as opposed to delta. (0.5772 = 0.333)This is why (no pun intended) we use wye-delta starters on large motors - it allows them to come up to speed at 1/3 power, before switching to full power on delta.
in low voltage connection in wye (star conncetion) 415v high voltage connection in delta 480v
There are various ways in which you can connect a three-phase transformer's primary and secondary windings, or in which you can connect three single-phase transformers to create a three-phase transformer bank. For example: wye-wye, wye-delta, delta-delta, delta-wye, etc.For each connection, there is a natural phase shift between the primary and secondary line voltages. This is called the angular displacement (or 'phase displacement') of the transformer connection.If you wish to parallel two three-phase transformers, or two three-phase transformer banks, then their angular displacements must be the same (there are also other requirements not relevant to this answer).A vector group is a method of specifying a three-phase transformer (or transformer bank) method of connection and its angular displacement. Transformer connections from the same group can be paralleled. Those in different groups cannot
The power of a three-phase load is the sum of the three individual loads. It makes no difference whether they are connected in star (wye) or in delta.
the speed decrease if increasing load..in star connection the speed lower
Three-phase transformation can be obtained using two Transformers, by connecting them in what is known as an 'open delta' connection.
With a delta connection, picture a triangle. Each side of the triangle is a transformer or motor winding. Call the 3 corners of the triangle A, B, and C. There are only 3 wires except for a safety ground, which has no connection to, nor is any part of, the power transmission service lines.but for the star connection take our triangle above and use your wire cutters (literally) to cut the triangle apart at the corners. rearrange the three sides (transformer or motor windings) to form a Y. Where the three sides join in the centre, connect a fourth wire. Call this wire "neutral". Call the three ends A, B, and C. Connect the 3 supply service lines to A, B, and C.
There is really no advantage, the only purpose of having the variety is for motor manufacturer companies to be able to sell their product to customers if the building's electrical service is of a Delta of Wye configuration.