shunt trip coil used to trip the breaker automatically or manually.
The cost of a shunt trip breaker depends on the amperage and number of poles the circuit connected to it needs. The cost of the shunt trip over a conventional breaker is substantially more.
See the diagram linked below.
The way to detect if a shunt trip breaker is malfunctioning is to manually trip the breaker. The shunt is usually wired through a auxiliary relay. Make sure that before you trip the breaker that the load can be shut off without taking a production line etc. off line. Trip the auxiliary relay using a test jumper to activate the relays coil. The breaker's handle will move to mid throw and the load will disconnect from the supply power. If the breaker trips then it is working properly. If the breaker does not trip trouble shoot the circuitry that is used to trip the breaker. Usual problem is an open circuit.
Usually the breaker's shunt trip coil is tied to a corresponding current transformer that is sized to the amperage that is allowed to be passed through the breaker. These types of breakers can also be connected into a distribution monitoring device. If the monitor detects a phase reversal or phase loss or voltage rise or drop the breakers shunt trip coil is remotely energized and isolates equipment down stream from the fault. Shunt trip coil circuits are also used as safety circuits where the situation calls for only one breaker to be energized at a time. If the second breaker is inadvertently closed, this would allow both breakers to be on, the second breaker's auxiliary contacts that are an internally part of that breaker will close the safety circuit and energize the shunt trip in the first breaker to causing it to open. So as you can see the two wires could be part of many wiring configurations depending on what situation calls for.
An elevator shunt trip test checks the heat detector placement. It also monitors power and wiring diagram of an elevator.
shunt trip coil used to trip the breaker automatically or manually.
Yes a shunt trip breaker can be activated manually.
The cost of a shunt trip breaker depends on the amperage and number of poles the circuit connected to it needs. The cost of the shunt trip over a conventional breaker is substantially more.
Yes, you can. If your shunt trip is 120 volts, just get 120 volt from your panel and take it to your ansul normally open contacts than to your shunt trip braker. than when your ansul system trips it will trip your shunt braker.
No, when a shunt trip breaker trips, it opens the circuit and disconnects the voltage supply to the protected circuit.
Yes, but you need a power source, for the shunt trip coil voltage, in the circuit.
See the diagram linked below.
To wire a shunt trip breaker for testing, connect one terminal of the shunt trip coil to the breaker's trip terminal, and connect the other terminal to the source voltage. When a signal triggers the shunt trip coil, it will cause the breaker to trip as if there were a fault, allowing for testing without an actual fault condition.
A shunt trip breaker is reset the same way as an ordinary breaker, move the handle to the full off position and then to the full on position. First check the tripping circuit, sometimes a latch relay is used to hold the breaker shunt trip coil in the trip position. If this is the case then reset the latch relay first.
220V
Moulded breakers or shunt trip breakers - selection is defined by the current rating requirement.