Using the AWG for wire sizes only goes up to 4/0. After that the increases use MCM to size the wire. So your 262 MCM wire size will be same in AWG. There is no 262 MCM in the North American market place. It goes in 50 MCM increments starting at 250 MCM , 300 MCM, 350 MCM, 400 MCM right up to 2000 MCM cable.
250 mcm
250 MCM aluminum minimum
300 Amps if used for service entrance conductors. Table 310.15
There are different combination to obtain a current capacity of 1250 amps. A parallel run of #1250 MCM wires. A triple run of #600 MCM wire. The most flexible run would be with a quad run of #350 MCM wire.
250 MCM copper wire weighs approximately 0.311 pounds per foot.
A 250 MCM copper conductor with an insulation factor of 75 or 90 degrees C is rated at 255 and 290 amps respectively
Using the AWG for wire sizes only goes up to 4/0. After that the increases use MCM to size the wire. So your 262 MCM wire size will be same in AWG. There is no 262 MCM in the North American market place. It goes in 50 MCM increments starting at 250 MCM , 300 MCM, 350 MCM, 400 MCM right up to 2000 MCM cable.
250 mcm
If you use 250 or 300 MCM wire you will need a 2 1/2" weather head. If you use 300 MCM wire then you will need a 3" weather head.
1 MCM means 1000 circular mils, and a circular mil is the area of a circle with diameter 1 mil ( that is 1/1000 of one inch). In metric terms, 1 MCM = 0.5067 sq mm
In electrical wiring awg ( American wire gauge) goes to 4/0 as the largest size. then it goes to 250 mcn. MCN which stands for 1,000 Circular Mils. this system uses the cross sectional area of the wire as a measurement. typical mcm wire sizes start at 250 and go to 300,350,400,500,600, etc. 250 mcm is usually good for a 200 amp service in aluminum wire in Canada per code. American standards are not as high or as good as Canadian ones. 250 MCM Welding cable is the next size larger than the standard 4/0 cables used on most standard mag particle inspection machines. Increasing the cable size will reduce the heating effect on the cables and increase the available current. welding cables is one of the more common uses for bigger sized wires. 250 MCM Cable has a cross-sectional area of .199 square inches
In electrical wiring awg ( American wire gauge) goes to 4/0 as the largest size. then it goes to 250 mcn. MCN which stands for 1,000 Circular Mils. this system uses the cross sectional area of the wire as a measurement. typical mcm wire sizes start at 250 and go to 300,350,400,500,600, etc. 250 mcm is usually good for a 200 amp service in aluminum wire in Canada per code. American standards are not as high or as good as Canadian ones. 250 MCM Welding cable is the next size larger than the standard 4/0 cables used on most standard mag particle inspection machines. Increasing the cable size will reduce the heating effect on the cables and increase the available current. welding cables is one of the more common uses for bigger sized wires. 250 MCM Cable has a cross-sectional area of .199 square inches
250 MCM aluminum minimum
For a 400 Amp service with 500 MCM conductors, the minimum size grounding electrode conductor required would be 3/0 AWG copper or 250 kcmil aluminum based on the NEC Table 250.66.
300 Amps if used for service entrance conductors. Table 310.15
mcm