The cost of a shunt trip breaker depends on the amperage and number of poles the circuit connected to it needs. The cost of the shunt trip over a conventional breaker is substantially more.
shunt trip coil used to trip the breaker automatically or manually.
The way to detect if a shunt trip breaker is malfunctioning is to manually trip the breaker. The shunt is usually wired through a auxiliary relay. Make sure that before you trip the breaker that the load can be shut off without taking a production line etc. off line. Trip the auxiliary relay using a test jumper to activate the relays coil. The breaker's handle will move to mid throw and the load will disconnect from the supply power. If the breaker trips then it is working properly. If the breaker does not trip trouble shoot the circuitry that is used to trip the breaker. Usual problem is an open circuit.
Usually the breaker's shunt trip coil is tied to a corresponding current transformer that is sized to the amperage that is allowed to be passed through the breaker. These types of breakers can also be connected into a distribution monitoring device. If the monitor detects a phase reversal or phase loss or voltage rise or drop the breakers shunt trip coil is remotely energized and isolates equipment down stream from the fault. Shunt trip coil circuits are also used as safety circuits where the situation calls for only one breaker to be energized at a time. If the second breaker is inadvertently closed, this would allow both breakers to be on, the second breaker's auxiliary contacts that are an internally part of that breaker will close the safety circuit and energize the shunt trip in the first breaker to causing it to open. So as you can see the two wires could be part of many wiring configurations depending on what situation calls for.
A shunt trip breaker is installed like any other molded case breaker. The only difference is that it has an internal tripping coil that is usually connected to a C.T. The breaker is usually mounted in a MCC cabinet The top of the breaker is bolted to the MCC bus bars and the bottom of the breaker is connected to the load. The load conductors pass through the C.T.'s which induces a current into the circuit to trip the tripping coil in the breaker.
A shunt-trip coil is a built-in component of a shunt-trip circuit breaker. It is a magnetic coil that can be energized externally to make the breaker trip to shut off the flow of current. For instance, fire sprinklers are sometimes required in the top of elevator shafts in case of a fire in the shaft. If the sprinklers were to spray water on the electric controls in the elevator cab, people could be hurt or killed, either from electrocution or from the elevator malfunctioning. In these cases, a shunt-trip breaker is installed in the circuit feeding the elevator controls, and the fire alarm system sends a trip signal if it detects waterflow from the sprinkler system. This trips the breaker and removes power from the elevator cab. Once tripped, a shunt-trip breaker requires a person to reset it manually.
It works just like a normal circuit breaker with one additional function. A shunt-trip breaker also has a built-in magnetic coil that can be energized externally to trip the breaker. For instance, fire sprinklers are sometimes required in the top of elevator shafts in case of a fire in the shaft. If the sprinklers were to spray water on the electric controls in the elevator cab, people could be hurt or killed, either from electrocution or from the elevator malfunctioning. In these cases, a shunt-trip breaker is installed in the circuit feeding the elevator controls, and the fire alarm system sends a trip signal if it detects waterflow from the sprinkler system. This trips the breaker and removes power from the elevator cab. Once tripped, shunt-trip breakers require a person to manually reset them.
Yes a shunt trip breaker can be activated manually.
An elevator shunt trip test checks the heat detector placement. It also monitors power and wiring diagram of an elevator.
I can only assume that you are attempting to connect 480VAC coil from a elevator to a fire system in order to shunt the elevator. In order to do this you will need a shunt trip breaker rated for this use.
The cost of a shunt trip breaker depends on the amperage and number of poles the circuit connected to it needs. The cost of the shunt trip over a conventional breaker is substantially more.
shunt trip coil used to trip the breaker automatically or manually.
Yes, but you need a power source, for the shunt trip coil voltage, in the circuit.
No, when a shunt trip breaker trips, it opens the circuit and disconnects the voltage supply to the protected circuit.
A shunt trip breaker is reset the same way as an ordinary breaker, move the handle to the full off position and then to the full on position. First check the tripping circuit, sometimes a latch relay is used to hold the breaker shunt trip coil in the trip position. If this is the case then reset the latch relay first.
A secondary shunt releases (extra trip coil) is used forelectrical tripping of the circuit breaker by protectiverelays or manual control devices when more than onetrip coil is required.
220V