Without knowing full details of the site and the location of the ANSUL equipment, there are 3 main reasons for an accidental discharge:

  • The Automan unit is placed too close to a heat source and the compressed gas cartridges heated to a point where the foil seal burst (like a burst disc), setting off the system
  • The automatic detection line wire passes through a cable clamp within the Automan unit. If this clamp is not set correctly and the two grub screws are not tightened correctly, the cable can slip and activate the system.
  • If you have a disgruntled employee, they may have maliciously pulled the manual release mechanism. This is by far the most common reason for false activations.
User Avatar

Wiki User

βˆ™ 13y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Why did the ansul system discharge without a fire?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Why did your ansul system discharge without a fire?

Either the mechanical release mechanism was pulled by a disgruntled employee (most common reason for a discharge); the service/ maintenance schedule has not been followed and a fusible link has failed; the mechanism has failed within the Automan Unit.


Ansul system how to use?

ANSUL Systems operate automatically when fire linkages are connected and the tension lever is ON. ANSUL can also be deployed manually by pulling the handle.


Does concession trailers have to have an ansul system?

yes, if it has a hood it has to have a fire suppression system.


What does ANSUL stand for?

ANSUL is the brand name of a wet chemical fire suppression system manufacturer based in the US. The systems are commonly found in kitchens.


Who is the ansul r102 distributor kitchen fire suppression system for uk?

Telegan Protection LtdSealand Centre


What is an ansul system made with?

Ansul is a brand name for wet chemical fire suppression equipment found in kitchens of restaurants and hotels. The systems usually contain an automated activation system (via a heat rated fusible link) and a manual release mechanism. A low Ph fire suppression chemical (known as Ansulex, or R-102) is stored within agent tanks, and is fed through supply lines after actuation by pressurised Nitrogen or CO2 (stored in cartridge form) to discharge nozzles above appliances. Most of the system components are made from Stainless Steel for hygiene reasons. Ansul systems are very design specific and should only be designed, installed and maintained by authorised Ansul distributors and engineers.


What are 2 ways the Ansul systerm can be activated?

The Ansul system can be activated manually by pulling a manual pull station or automatically by a fusible link melting due to high heat, releasing the fire suppression agent.


What products does Ansul make?

Ansul is an Oakville, Ontario based company which manufactures and distributes fire protection gear such as fire extinguishers, as well as fire hazard outfits for commercial businesses.


Who is the Ansul R102 Distributor Kitchen Fire Suppression System for Ireland?

Action Fire Security Services Ltd.Bridges Industrial EstateRed Cow, Naas RoadDublin 22


How Much for ansul 3 gallon fire system UL 300 listed single tank installed in Boston Non union labor?

2195.00


How is the wiring diagram for disconnecting an outlet and a exhaust fan when a Fire Suppression System is activated?

My brother has a Restaurant and days ago, he upgraded the Fire Suppression System (also named Ansul System). So the ansul, has only a microswitch that has only 3 leads (two contacts, one "nc" and "no"). Now, how is the diagram to interconnect this microswitch with othe elements (electrical) to disconnect one outlet that is located under the hood plus the fan, as per code here in the city? The guy who install the Ansul did only the mechanical part. I'm an electrician and I would like to do the electrical connections.


Can you use molded breakers instead shunt trip breakers for an Ansul fire suppression system?

Moulded breakers or shunt trip breakers - selection is defined by the current rating requirement.