Every electrical component has a rated steady state current specified at a certain ambient temperature (in most cases 40 degC). This is the "continuous" current carrying capacity of the component at the rated operating temperature. If the actual ambient tempertature in the operating area is higher than the rated ambient temperature then the "continuous" current carrying capacity of the component is reduced. This happens due to the physical property of metals which causes the resistance of the matal to increase with the increase in temperature. Example: A component rated at 8A @ 40 deg C will be rated at >7A at 50 deg C. At 50 deg C you can still pass all 8A through the component but it will genenrate more heat and can eventually burn out.

User Avatar

Wiki User

16y ago

What else can I help you with?

Related Questions

What is current value after derating factor considered?

Once derating factor is considered the size of cable for perticular electrical load increased by the multipling factor.i,e if 2.5MM2 cable is capable to carry 14amp. of current in general then with 40% of derating fator it can carry only 8.4amp.


What information can be found on a wire derating chart?

A wire derating chart provides information on how much current a wire can safely carry based on factors such as wire size, insulation type, and ambient temperature.


How many current carrying conductors are allowed in a raceway before derating?

You can put three ccc's in a conduit (any size conduit) before you derate. Keep in mind that for single phase loads (lighting, receptacles) the neutral is also counted as a current carrying conductor. This derating factor does not apply to nipples 24 inches long or less. See NEC Table 310.15(B)(2)(a) for full details on derating regarding ccc's.


How do you calculate derating factor for cables?

The derating factor for cables is calculated by considering various environmental factors such as ambient temperature, grouping of cables, and installation conditions. First, determine the cable's current-carrying capacity based on its specifications. Then, apply correction factors from relevant standards or tables for each influencing factor, multiplying these factors together to obtain the overall derating factor. Finally, multiply the original capacity by the derating factor to find the adjusted capacity for safe operation.


What is derating factor of battery?

batteries derating factor will change ,depends upon the temperature& cable size which arelinked with batteries bank.


How many current carrying conductors can you have in a conduit before you have to start derating amparage?

The number of current-carrying conductors allowed in a conduit before derating is specified by the National Electrical Code (NEC). Generally, if you have more than three conductors in a conduit, you need to start derating the ampacity of the conductors. Specifically, for more than three conductors, the ampacity of each conductor must be reduced based on the number of conductors present. For example, with 4 to 6 conductors, the ampacity is typically reduced to 80%, and with 7 to 9 conductors, it’s reduced to 70%.


The calculation used to determine amperage of a conductor based on the total number of conductors in a conduit is called A derating B voltage drop C conduit fill D conductor fill?

derating


What is the derating?

Derating factor depends on ambient temperature & how u r laying the cable ie., in Air,Duct,Burried. normally the current carring capacity of a perticular cable is calculated at 40*c, but if u lay the cable in air then it includes the temparture around it,if it increases more the 40*c then the conductor gets heated up by increasing the resistance in it thus the current carring capacity of a given cable decreases, so we will derate the cable The derating factor of induction motor is the ratio of the calculated output power to the rated power


What is derating factor in case of diesel engines?

air flow speed


Definition of derating?

The verb derating means to assess the value of (some types of property, such as agricultural land) at a lower rate than others for local taxation; operation of a machine at less than its rated maximum power in order to prolong its life.


What is the current carrying capacity of ACSR conductor at 45 degree ambient?

The current carrying capacity of an ACSR conductor is typically specified by the manufacturer and depends on factors such as conductor size, insulation type, and ambient temperature. Operating at a 45-degree ambient temperature may lead to a slight derating of the conductor's current carrying capacity compared to standard conditions, so it would be best to consult the manufacturer's specifications for accurate information.


What ampacity column are you allowed to use for derating using thhn wire?

When derating THHN wire, you typically refer to the ampacity column in the National Electrical Code (NEC) Table 310.16 (or its equivalent in local codes). This table provides the allowable ampacity for various wire types at different temperature ratings and installation conditions. For derating, you'll adjust the ampacity based on the number of conductors in a raceway, ambient temperature, and insulation type, ensuring compliance with NEC guidelines. Always consult the latest version of the NEC and local amendments for accurate information.