208 volts is the phase to phase voltage on a three phase low voltage system. In a split single phase service, the voltage is 120/240. In a three phase service, the voltage is 120/208. This is due to using a different transformer configuration. In the above, the first number is the phase to neutral reading, and the second is the phase to phase reading. For example, 120/240 and 120/208 both provide 120v on standard receptacles, but when using a dryer, or hot water heater, for example, that appliance would be using 240v or 208v, respectively.
The key to understanding this is "Phases" and supply configuration.
there r 2 types of supply Transformers, "Y" and "delta" /_\ = triangle
Each one produces 240V single phase across each coil.
In a Y config connecting to 2 legs of the Y produces output from 2 coils that r 120° out of phase. The resulting voltage is 208 volts instead of 240V.
If u connect to a leg and the center u get output from 1 coil only = 120V.
This is why 208 labeling is seen as 208Y/120
Normally, all 3 legs r used and the result is 208V 3 phase.
For a Delta configuration connecting to any 2 end points yields output from only one coil which is 240V single phase. 120v is obtained by center tapping that coil and connecting center to end.
Voltage Stabilizer is also called Automatic Voltage Stabilizer or AC Voltage Stabilizer or Voltage Regulator. Actually an automatic voltage stabilizer is designed to automatically maintain a constant voltage level, with protections of equipment against voltage surges, over voltage, under voltage, smoothing impulsive noise.
The two resistor voltage divider is used often to supply a voltage different from that of an available battery or power supply. In application the output voltage depends upon the resistance of the load it drives.
What is a card inside a notebook that converts voltage to CPU core voltage?
The purpose of an adjustable voltage regulator is to have a regulator that can give out variable voltages. This is in contrast to a fixed voltage regulator which only outputs one voltage, which it is rated for. To allow for adjustable voltage, usually the resistors on the output of the regulator just need to be swapped for different values to give differing output voltages.
7805is a voltage regulator integrated circuit. It is a member of 78xx series of fixed linear voltage regulator ICs. The voltage source in a circuit may have fluctuations and would not give the fixed voltage output. The voltage regulator IC maintains the output voltage at a constant value. The xx in 78xx indicates the fixed output voltage it is designed to provide. 7805 provides +5V regulated power supply. Capacitors of suitable values can be connected at input and output pins depending upon the respective voltage levels.Pin Diagram:Pin Description:Pin NoFunctionName1Input voltage (5V-18V)Input2Ground (0V)Ground3Regulated output; 5V (4.8V-5.2V)Output
208 voltage star refers to a three-phase electrical system where the voltage between any two phases is 208 volts. This type of system is commonly used in commercial and industrial applications to power machinery and equipment. Voltage configurations such as 208Y/120V or 208/120V are typical examples of 208 voltage star systems.
122/208
From line-to-line (any two of the three leads) voltage or 'line voltage', the voltage is 208 V. The line-to-neutral (one of the three leads and the neutral conductor), or 'phase voltage', is 120 V.
208 is a three phase wye connection voltage. To obtain the each individual coil voltage the 208 is divided by 1.73 which equals to 120 volts. Hence you have 3 phase 208 voltage on the phase legs and 120 volts to the wye point which is grounded. This same formula is used on any 3 phase system. 600/347, 480/277, 208/120.
Yes. Usually can be found in commercial establishments.
No a 208 volt outlet does not need a neutral. 208 volts is the line voltage between any two legs of a three phase 208 volt system.
No. A 277 volt ballast needs the correct voltage to operate. The 277 voltage is derived from the star point voltage of a 480 volt three phase system (277/480). The 208 voltage is a three phase line voltage whose star-point voltage is 120 volts (120/208).
No, 230 and 208 are not the same as 220. 230 and 220 are close in value but not identical, while 208 is a different voltage level. It's important to ensure the correct voltage is used when operating electrical equipment to prevent damage or safety hazards.
To convert from Amperes to kVA, you can use the formula kVA = (Voltage x Amperes) / 1000. Plugging in the values, kVA = (208 V x 2160 A) / 1000 = 449.28 kVA.
You don't. The cook top was designed to operate on 208 volts. This is the voltage needed to get the elements up to their rated wattage to do the cooking. Higher wattage appliances do not operate on the lower voltage because of the size of the wire that is needed to feed the appliance.
To meter a 208V load using only one phase, you would typically measure the voltage of that phase to neutral and then multiply it by the square root of 3 (approximately 1.732) to get the line-to-line voltage. In this case, the line-to-line voltage for a 208V load on one phase would be approximately 360V. This calculation is based on the relationship between line-to-neutral and line-to-line voltages in a three-phase system.
I have 12 amps 208/3/60 what would the amps be @ 440/3