Best Answer

The H1 and H2 symbols on a transformer designates the two coil ends of the primary winding on a transformer. The symbol is the same regardless if the transformer is step up or down.

Answer

In North America, a transformer's high-voltage windings are identified by the letter H, and the low-voltage windings by the letter X. The 'start' of a winding is allocated an odd number, and the 'finish' of a winding is allocated an even number. For example, H1-H2 represent the start and finish terminals of a high-voltage winding, and X1 - X2 represent the start and finish terminals of a low-voltage winding.

For a distribution step-down transformer, with the low-voltage terminals facing you and the high-voltage terminals on the far side of the transformer, terminal H1 is, by convention, alwayson the left-hand side of the transformer.

When terminal H1 'goes positive' (i.e. is subjected to the positive half-cycle of the AC waveform), X1 also 'goes positive'.

The identification of a transformer's terminals is important in order to determine the polarity of a transformer. Knowing a transformer's polarity is essential if two Transformers are to be connected in parallel with each other.

User Avatar

Wiki User

13y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

14y ago

In a step down transformer the "H1" terminal is one of the line side connections.

If you did not already know this answer, I would highly recommend that you obtain the services of a qualified electrician to hook it up. Electricity is dangerous if not properly installed!

This answer is:
User Avatar

User Avatar

Wiki User

12y ago

In North America, 'H' represents a high-voltage terminal, whereas 'X' represents a low-voltage terminal. Odd number subscripts represent the 'start' of a winding, whereas even number subscripts represent the 'finish' of a winding. For example, the terminals of a high-voltage winding might be marked H1-H2, H3-H4, etc., depending on the number of high-voltage windings.

For an unmarked transformer, when facing the transformer such that the high-voltage terminals are on the far side of that transformer, is the terminal on the left-hand side is normally then labelled H1.

This answer is:
User Avatar

User Avatar

Wiki User

14y ago

The H1 designation refers to a connection on the primary side of the transformer. On a three phase transformer the A phase would be connected to the H1 terminal. Likewise B phase to H2 and C phase to terminal H3. Secondary terminals on this transformer will be designated X1, X2 and X3.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: When conectring a step down transformer what is H1?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

What is the line side of the 3 phase transformer?

The primary line side of a 3 phase transformer should be marked H1, H2, H3. The line side is the incoming voltage that you want to step up or step down or isolate.


What electrical phase does H1 denote?

H1 is a terminal designation on the primary side of a transformer. The counter part to this terminal is H2. These two terminals are the connection points for the primary coil of the transformer.


Why do you use Two Winding run and start winding in the single phase motor?

Any transformer uses a minimum of two windings to change the voltage value. The primary side of the transformer is usually connected to the existing voltage. The secondary side of the transformer is usually connected to the load, who's voltage could be higher or lower voltage than the primary voltage.If the secondary voltage is increased the transformer is known as a step up transformer and if the secondary voltage is decreased the transformer is known as a step down transformer.The transformer terminal markings for the primary are H1 and H2 on a single coil primary and H1 to H4 on a dual voltage primary winding. Like wise the secondary terminal markings are X1 and X2 on a single coil secondary and X1 to X4 on a dual voltage secondary winding.


How do you know if a transformer is a step up transformer?

You will most likely see a 'step-up' transformer on neon signs. The next time you're at a restaurant or bar, look at their neon sign. You'll see a black box (4" x 4" x 6"w) connected to the sign (usually). This is the transformer, and it takes 120 volts AC and steps it up to 7500 to 10,000 volts AC. This excites the neon gas and causes it to glow.AnswerA step-up transformer transforms voltage to a higher level. Like 120 volts to 277 volts.AnswerIt is type of transformer which is used to step up the voltage from low to high value in order to make it applicable for high rated appliances.Not only for high rated appliances but also for transmission in power distribution systems. It is critical in this role. Power distribution systems depend heavily on step-up transformers to generate the high voltages needed for more efficient long-distance power distribution. (And yes, there are step-down transformers at the other end to make the voltages more "user friendly" and less dangerous.)


How does a step up and step down transformer work?

Transformers rated 1 KVA and larger single phase,3 KVA and larger three phase can be reverse connected without any adverse effects or loss in KVA capacity. The reason for this limitation in KVA size is, the turns ratio is the same as the voltage ratio. On transformers rated below 1 KVA single phase, there is a turns ratio compensation on the low voltage winding. This means the low voltage winding has a greater voltage than the name plate voltage indicates at no load. Terminals on a single wound transformer, primary side are labeled H1,and H2 and on the secondary side X1 and X2. Just reverse the input voltage to the X1 and X2 terminals and the take the load off of the H1 and H2 side.

Related questions

What is the line side of the 3 phase transformer?

The primary line side of a 3 phase transformer should be marked H1, H2, H3. The line side is the incoming voltage that you want to step up or step down or isolate.


What the purpose of the H1 terminal on a transformer?

The terminals H1 and H2 an a transformer indicate the primary side of the transformer. The secondary side is usually identified as X1 and X2.


Can 240 volts be converted to 110 volts?

Yes , with a step down transformer. 240 volts into the primary side H1 and H2 which is stepped down to 120 volts on the secondary side, X1 and X2.


What electrical phase does H1 denote?

H1 is a terminal designation on the primary side of a transformer. The counter part to this terminal is H2. These two terminals are the connection points for the primary coil of the transformer.


Why do you use Two Winding run and start winding in the single phase motor?

Any transformer uses a minimum of two windings to change the voltage value. The primary side of the transformer is usually connected to the existing voltage. The secondary side of the transformer is usually connected to the load, who's voltage could be higher or lower voltage than the primary voltage.If the secondary voltage is increased the transformer is known as a step up transformer and if the secondary voltage is decreased the transformer is known as a step down transformer.The transformer terminal markings for the primary are H1 and H2 on a single coil primary and H1 to H4 on a dual voltage primary winding. Like wise the secondary terminal markings are X1 and X2 on a single coil secondary and X1 to X4 on a dual voltage secondary winding.


How do you know if a transformer is a step up transformer?

You will most likely see a 'step-up' transformer on neon signs. The next time you're at a restaurant or bar, look at their neon sign. You'll see a black box (4" x 4" x 6"w) connected to the sign (usually). This is the transformer, and it takes 120 volts AC and steps it up to 7500 to 10,000 volts AC. This excites the neon gas and causes it to glow.AnswerA step-up transformer transforms voltage to a higher level. Like 120 volts to 277 volts.AnswerIt is type of transformer which is used to step up the voltage from low to high value in order to make it applicable for high rated appliances.Not only for high rated appliances but also for transmission in power distribution systems. It is critical in this role. Power distribution systems depend heavily on step-up transformers to generate the high voltages needed for more efficient long-distance power distribution. (And yes, there are step-down transformers at the other end to make the voltages more "user friendly" and less dangerous.)


How does a step up and step down transformer work?

Transformers rated 1 KVA and larger single phase,3 KVA and larger three phase can be reverse connected without any adverse effects or loss in KVA capacity. The reason for this limitation in KVA size is, the turns ratio is the same as the voltage ratio. On transformers rated below 1 KVA single phase, there is a turns ratio compensation on the low voltage winding. This means the low voltage winding has a greater voltage than the name plate voltage indicates at no load. Terminals on a single wound transformer, primary side are labeled H1,and H2 and on the secondary side X1 and X2. Just reverse the input voltage to the X1 and X2 terminals and the take the load off of the H1 and H2 side.


How do the symbols of additive transformers differ from subtractive polarity?

Using North American standards, when terminal X1 is diagonally opposite terminal H1, the transformer is additive.


What wires conductors would go under x lug in a transformer?

The primary side of a transformer is identified as the H side, eg. H1,H2,H3,H4. The secondary side of a transformer is identified as the X side. Eg. X1, X2. Usually X1 goes to a fuse and then to the load, X2 is usually the neutral side and is grounded to the body of the transformer.


What is the default styling for h1 HTML tag?

The H1 tag is used to display Headings in HTML. <H1> Hi this is a H1 header </H1> would display like = Hi this is a H1 header =


How do you determine the polarity of transformer windings?

They are marked on the transformer. H1 and H2 primary, X1 and X2 secondary. Dual voltage primary H1, H3 H2, H4, Dual voltage secondary X1, X3, X2, X4.Additional Answer for Unmarked TransformerFor a completely unmarked transformer, a continuity test will confirm which terminals belong to which windings, and a resistance test will identify the high-voltage (higher resistance) and low-voltage (lower resistance) windings. In North America, HV winding terminals are identified by the letter 'H' and LV windings by the letter 'X'. For a two-winding, four terminal, transformer, to test for polarity, the transformer should be orientated so that the HV windings are on the far side of the transformer, and the LV windings are on the nearest side. By convention, the left-hand HV terminal is then marked H1, and the right-hand terminal is marked H2. The LV terminal adjacent to H2 is then connected to terminal H2, so that both the HV and LV windings are in series. A voltmeter is then connected between the LV terminal adjacent to H1, and the H1 terminal itself. A low-voltage supply is then connected across the HV windings (i.e. between H1 and H2). If the voltmeter registers a voltage higher than that applied to the HV windings, then the transformer is of additive polarity, and the LV terminal adjacent to H2 should be marked X1 and the LV terminal adjacent to H1 should be marked X2. If, on the other hand, the voltmeter reading is less than the applied voltage, then the transformer is of subtractive polarity, and the LV terminal adjacent to H2 should be marked X2, and the terminal adjacent to H1 should be marked X1.By convention, when terminal H1 'goes positive' during the AC sine-wave, then terminal X1 should also 'go positive'.A similar process applies to multi-winding multi-terminal transformers. Again, the windings of such transformers must have their terminals identified first -a simple continuity test will reveal these. The rule is that an odd number (e.g. H1, etc.) represents the 'start' of a winding, and an even number (e.g. H2) represents the 'end' of a winding. Again, a simple resistance test will identify the high-voltage (higher resistance) and low-voltage (lower resistance) windings.For UK transformer, HV windings are identified as A-B, etc., and LV windings as a-b, etc.


how do you connect a dry type transformer to a 250v wye system to get 120v.the primary has h1-4 and the secondary x1-4.?

Dry type transformers should work fine with a primary H1-4 and X1-4. If it's not working check to make sure that you're really getting 250V.